It has 4 different onesView attachment 2553116 View attachment 2553117
I know that's right! Do you know what the other dimensions are on nm?
It has 4 different onesView attachment 2553116 View attachment 2553117
I know that's right! Do you know what the other dimensions are on nm?
In 1/2" PVC too. Will there be any sched 80 in there, yikes.I'd say that pulling UF in PVC is one of the toughest pulls there are.
In 1/2" PVC too. Will there be any sched 80 in there, yikes.
Its piped all the way. TA to TA. FS box to panel. I only had to pipe it, due to the steele structure in the crawlspace. Hence, no where to stapleAs noted in post 17 https://forums.mikeholt.com/threads/12-2-uf-wire-in-1-2-pvc.2555307/post-2599671 , if you have a _sleeve_ rather than a _raceway_ you might be kosher.
Loose THHN requires a raceway. But UF is a cable assembly, and could simply be stapled to the joists/studs/etc. In which case the PVC might simply be there for mechanical protection or as a convenient way to support the UF.
You are not permitted to piece together a raceway around loose wires; you have to fit all the bits together and then pull the wires in. But you can assemble a sleeve in whatever fashion makes the most sense mechanically. A raceway needs to be complete from one box to another; but a sleeve can end in free air (possibly with some protection for the exiting cable).
There are probably other requirements that I am forgetting about the differences between the two.
So, do you have a PVC sleeve or a PVC raceway?
-Jon
This is where it's gray for me.As noted in post 17 https://forums.mikeholt.com/threads/12-2-uf-wire-in-1-2-pvc.2555307/post-2599671 , if you have a _sleeve_ rather than a _raceway_ you might be kosher.
-Jon
It has nothing to do with heat that would be derating for more than 3 CCC in the raceway. The fill rule is to ensure that the cable can be pulled in without damage.I'm just going to push it with thhn. Just wasn't aware of uf not being acceptable in 1/2". Kind of a nuisance when they consider the diameter of the sheathing as one conductor. I get pipe fill, but it shouldn't be calculated in for heat measures. At least not when the sheathing is included as a conductor in whole, which produces no heat. Pretty sure its rated at 190°. Theres no way that that wire is getting that hot unless their is a malfunction on the appliance, which the gfi that I installed would trip it before allowing it to draw over 20 amps
Ground isn't a CCC. I literally pieced every single pipe and fitting together one by one. Nice, neat, and safe. I guess the "removal" of the wire would be the only obstruction which goes against NEC?It has nothing to do with heat that would be derating for more than 3 CCC in the raceway. The fill rule is to ensure that the cable can be pulled in without damage.
What is the code for pipe fill that insists it's for the damage of installation and not heat? Not doubting you. Just learningIt has nothing to do with heat that would be derating for more than 3 CCC in the raceway. The fill rule is to ensure that the cable can be pulled in without damage.
The derating of CCC's accounts for heat, based on a function of fill.What is the code for pipe fill that insists it's for the damage of installation and not heat? Not doubting you. Just learning
Right here:What is the code for pipe fill that insists it's for the damage of installation and not heat? Not doubting you. Just learning
300.17 Number and Size of Conductors in Raceway. The number and size of conductors in any raceway shall not be
more than will permit dissipation of the heat and ready installation or withdrawal of the conductors without damage to the
conductors or to their insulation.
Oh but I see your point. So technically it's not heat even though they say it is? So confusingRight here:
As far as derating for more than 3 CCC's in a raceway the NEC doesn't care if it's ½" or 6" conduit, you get no credit for the additional air in a larger raceway.
"It's what's for dinner.""Heat and ready"
Why are you putting uf inside of conduit if you are in a crawl space?It was all I had on me and I was by myself. I pieced it together in the crawl space and didnt damage the wire. Last time I'll ever do this. I just wanted to make sure I dont have to go back out and repull it in thhn, because I will if I have to
Because its underneath a trailer that has a steel bottom. nothing to staple to.Why are you putting uf inside of conduit if you are in a crawl space?
Beam clamps and zip ties are your friend next time.Because its underneath a trailer that has a steel bottom. nothing to staple to.