No you cant parallel 12awg conductors, too small.
they wouldnt be parrelled if they are only tied at the panel, the other ends will be going to seperate loads.
No you cant parallel 12awg conductors, too small.
Got a picture? I missed something.they wouldnt be parrelled if they are only tied at the panel, the other ends will be going to seperate loads.
Got a picture? I missed something.
I see.I dont have any pictures, but parrelled conductors are paired up and tied togther at both ends to double up the ampacity, what I am suggesting is just tieing the two conductors together in the panel and they will "Y" off to seperate loads, its no differnt than terminating the wires in a junction box as Pierre pointed out earlier, I just figgured it would be easier to do at the panel and not have to climb around in an attic or crawlspace to tie them together.
Edit- an example would be running 12-3 to a ceiling fan to operate the fan seperate from the lights but fed from the same circuit.
I'm thinking the homeruns are 12-3 w/G, but the loads are calculated to need 2 breakers. Eliminating one wire might cause a calculated overload.Some one help me please.. I guess I do not understand. 12-3 nm or what ever... black, red, white.... For the AFCI you want a hot, neutral and ground.. right?? Strip the red conductor at panel board and at first outlet.. Black, white, bare.... What am I doing wrong?? I must be missing something? I've never installed AFCI... have not touched residential in years...
I see.
But wouldn't you think the circuit has been sized for the load? Won't you now overload the breaker?
Some one help me please.. I guess I do not understand. 12-3 nm or what ever... black, red, white.... For the AFCI you want a hot, neutral and ground.. right?? Strip the red conductor at panel board and at first outlet.. Black, white, bare.... What am I doing wrong?? I must be missing something? I've never installed AFCI... have not touched residential in years...
I see you did mention it and, like you said, maybe it would work for a few select circuits.I touched on that on post #9, its just a suggestion to save some labor and material where he can, I may work for a few of the runs, it may not work for any of them, it just depends on how they divided up the loads. If they ran one bedroom off the black and another off the red, you could probably tie them together without any problems.
I would think it poor design to have all of the circuits calculated at 1/2 load capacity in a house.
People calculate loads in a dwelling unit?
News to me.:grin:
You still putting in those 60 amp panels?:grin:People calculate loads in a dwelling unit?
News to me.:grin:
depending on how much load you have on a circuit, couldnt you just tie both the black and red together on one breaker? if its a homeline panel, you could just double land them on the breaker to tie them together.
Gee look at the problems 1 idiot inexperienced hack causes, Look at all the time spent by others to fix his mess.
That is the problem there , someone who had no idea of what was going on and now the clean up starts. We are going to change out the panel to a siemensand have to go with a 2-pole arc-fault, even the state inspector agreed at least we have him on our side.
I wonder if the inspectors should start checking 3 wire circuits and ask the EC If they plan to use AFCI's. OR just put a note on the inspection card. " AFCI's reguired even for Multiwire circuits"Gee look at the problems 1 idiot inexperienced hack causes, Look at all the time spent by others to fix his mess.
That is the problem there , someone who had no idea of what was going on and now the clean up starts. We are going to change out the panel to a siemensand have to go with a 2-pole arc-fault, even the state inspector agreed at least we have him on our side.
depending on how much load you have on a circuit, couldnt you just tie both the black and red together on one breaker? if its a homeline panel, you could just double land them on the breaker to tie them together.