To all of you who responded... Thanks! I had forgotten to subscribe to this thread through e-mail notification, so I was not aware that anyone had answered the original question.


If you have many threads you are subscribed to, especially if they are very active threads, that method will fill your inbox. I prefer to periodically go to the quick links drop down menu at top of most pages and select subscribed threads. Then you can easily see which ones have new posts
 
I think Rob's point was that you can put a 20A receptacle on a 15A individual branch circuit, per 210.21(B)(1).

I think it is funny that the NEC "allows" a single 20 amp receptacle on a 15 amp individual branch circuit in 210.21(B)(1) but then turns around and prohibits any receptacle greater than 15 amps on a 15 amp branch circuit supplying two or more receptacles in 210.21(B)(3).

I assume that when I see a single 20 amp receptacle on an individual branch circuit, I will have a 20 amp branch circuit. But then again, I have learned that everyone doesn't design, wire, and install the same way. :rant:
 
I think it is funny that the NEC "allows" a single 20 amp receptacle on a 15 amp individual branch circuit in 210.21(B)(1) but then turns around and prohibits any receptacle greater than 15 amps on a 15 amp branch circuit supplying two or more receptacles in 210.21(B)(3).

I assume that when I see a single 20 amp receptacle on an individual branch circuit, I will have a 20 amp branch circuit. But then again, I have learned that everyone doesn't design, wire, and install the same way. :rant:

I think for the most part you will not see this as a standard installation practice even though it's permitted by the NEC. What you will see quite often is a 40 amp range circuit with a 50 amp single receptacle and a 50 amp range cord since there really is no standard 40 amp range cord.
 