I have never known it as half phase.
My apologies. I'd hoped that the smilies would make it clear that I was joking.
Jon
I have never known it as half phase.
Likewise!My apologies. I'd hoped that the smilies would make it clear that I was joking.
Jon
Yes, I understand, but I and the meter engineers are trying to figure this out exactly.The voltages on the two lines are 120° apart. The CTs tell the meters what the current is and what its phase relationship is to the line voltage. The current times the voltage in absolute value terms is the apparent power. The part of the current that is in phase with the voltage times the voltage is the real power.
Would you be able to post a sketch? I don't quite follow your text description.211009-045 EDT
In a 3 wire system consider one wire as a reference. Take two wattmeters and connective the appropriate (meaning to get correct phasing) one voltage wire of each wattmeter to any line to be assumed to be a common, and connect the other voltage wires, one of one meter to a "hot wire" and the other volt wire to the other "hot wire". Then take each wattmeter current coil and put it in the "hot" line associated with the voltage coil of that meter. Again appropriate phasing. The sum of the two wattermeter readings is the total power to the loads whatever they may be.
I believe this is discussed in M. B. Stout's book on "Electrical Measurements".
.
I do have a neutral landed on the meter. The software shows all the voltage values and they are correct. How did you arrive at 1800?The meter must have a voltage reference to neutral in addition to the voltage reference to each 'hot' to meter correctly.
If the meter is only measuring line to line voltage, then it can't even meter power correctly, let alone apparent power.
Imagine a customer with only resistive loads. If the meter only measures line to line voltage, then a customer could draw 10A L-L (2080W) or 10A L-N on each leg (2400W) but I am pretty sure in the latter case the meter would only register 1800W.
-Jon
I have a neutral and the meter is fully capable of phase angle and real power display. My problem is the apparent is all over the place and I can't reconcile my V and I reading to its apparent power reading.That answers OP's question, IMO. If no reference to the common (neutral) his metering is only going to be accurate for line to line loads.
He does need something that compares phasing of voltage to current to read real power, just multiplying current by amps will give him the apparent power he mentioned.
Imagine this scenario: The only load is 10A, say a dryer heating element. The apparent power is 10*208= 2080 VA. Now say the load is 2 10A 120V devices, say two hair driers that happen to be on opposite legs. here S = 2*120*10 = 2400 VA. The pair of CT's can each indicate 10A yet there are two different VA values.
My conundrum is how does a metering device calculate S when there can be different V values?
This is my scenario exactly. In regards to neutral current, the only way I see to do this is to measure neutral current, call that all 120V load, then subtract that from the CT value and call that 208V load.It's called single phase for historical reasons. I prefer the term "open-wye".
What it really is, is two out of three of the phase wires from a 3-phase wye system, that are 120 degrees out of phase. Most of the loads in each dwelling unit are 120V phase-to-neutral loads (lighting and receptacles), while a select few loads are dual-rated to work on either 208V or 240V. Like heating elements in ovens, stoves, and clothes dryers, and A/C. Unlike a 120/240V system where balancing all loads will eliminate neutral current, a 120/208V open-wye will have to have current on the neutral any time there are 120V loads, even with balancing.
You commonly see this on apartment buildings, where the site as a whole gets the full 3-phase supply, and each dwelling unit gets two out of three phases from it. The common loads panel likely gets a full three phase service. Each dwelling unit gets a "single phase" (open wye) service, with staggered pair of phases across the system. Such that remainder-1 unit numbers (1, 4, 7, 10 etc) will get phases AB, remainder-2 unit numbers (2, 5, 8, 11 etc) get phases CA, and the divisible-by-3 unit numbers (3, 6, 9, 12 etc) get phases BC.
I do have a neutral landed on the meter. The software shows all the voltage values and they are correct. How did you arrive at 1800?
The power meter measures voltage of both lines including the phase angle. It also measures the current in both lines including the phase angle. What more does it need to calculate the true and apparent power?This is my scenario exactly. In regards to neutral current, the only way I see to do this is to measure neutral current, call that all 120V load, then subtract that from the CT value and call that 208V load.
This is my scenario exactly. In regards to neutral current, the only way I see to do this is to measure neutral current, call that all 120V load, then subtract that from the CT value and call that 208V load.
Jon, that helps a ton, I think I can see a solution here.The metering device can figure this out because it doesn't simply measure RMS current or RMS voltage; the meter also measures the phase angles.
In the most common setup, the meter will measure the 2 phase-neutral voltages and the 2 phase currents. The meter is almost certainly measuring _instantaneous power_ and accumulating the energy used over time, but this is better understood if you think of the system as measuring the phase angles.
In the example you just gave, when you have two 120V L-N resistive loads, the current is exactly in phase with the supplied 120V. When you have a single 208V L-L load, the current is exactly in phase with the supplied 208V, which has a _different_ phase then the 120V L-N.
So in the first case the meter will be measuring
2 * 10A * 120V * 1.0 = 2400 W (2 power meter elements * 10A * 120V * 1.0 power factor)
In the second case the meter will be measuring
2 * 10A * 120V * 0.866 = 2080W (2 power meter elements * 10A * 120V * 0.866 pf)
Hope that helps.
Jon
Jon, that helps a ton, I think I can see a solution here.
You are saying in essence the meter is looking at Vln and then applying the phase shift (30*) if it sees the I out of phase with the V? That seems to be a valid way to differentiate the source voltage for a current. How about when there is a mixed voltage load, resistive? Still just the same, apply the phase angle, whatever it is? I guess that then also applies to a mixed reactive load, say a dryer motor? Again, just measure V and I and apply the pf?
Edit: apply pf, I mean cos(30) regardless of reactance as this is apparent power.
The simple answer is that the meter is sensitive to phase angle between the line current and the reference voltage.Yes, I understand, but I and the meter engineers are trying to figure this out exactly.
BTW, I have a neutral. I saw this mentioned in a later response.
Imagine this scenario: The only load is 10A, say a dryer heating element. The apparent power is 10*208= 2080 VA. Now say the load is 2 10A 120V devices, say two hair driers that happen to be on opposite legs. here S = 2*120*10 = 2400 VA. The pair of CT's can each indicate 10A yet there are two different VA values.
My conundrum is how does a metering device calculate S when there can be different V values?
Under the hood, what the metering element is measuring the product of voltage * current moment by moment. Not RMS voltage, RMS current and phase angle, but the _instantaneous_ values of voltage and current and taking their product. But the integral of this product is directly related to the phase angles.
-Jon
That seems to be a sticking point. If they are not in phase then they can't be single phase.If you consider just the current on each of the hot leads with respect to the 120V line to neutral voltage you will see that the current is not in phase with the line to neutral voltage. That reduction in real power lets the sum of the two 120V power calculations to equal the single 208V power calculation.
You have guessed my next step in the process, the mixed voltages and the addition of reactance.If you have a mixed load (some L-L, some L-N) or mixed load power factors (some resistive, some inductive) the same thing applies. Both of the sensors will see some current with some phase angle and will calculate the total power from that.
That seems to be a sticking point. If they are not in phase then they can't be single phase.
120V load with inductance: Say 10* lag. S should remain unchanged, it is apparent power. As this lagging phase angle is introduced, how does the meter logic work? S should be simply V*I, but since the V and I waveforms aren't coincident how does the meter know which I peak to use for this calculation? Adding in the phase angle component will reduce the apparent power calculation. If the calculation is made at VLNmax, the I value will be < Imax. Since there is only one current waveform in this case, does the meter just grab the Imax value irrespective to phase angle, then do the math?
208V load with inductance: Same as 120V, single waveform, grab Imax and do the usual math?
Mixed voltages with inductance: This one has me totally baffled. Since there are two I waveforms I don't know how the meter would associate the two Imax's with the appropriate voltage. Related to that, how does it calculate phase angle between V and I when there are two waveforms of each present?
Your obsession with this terminological detail crossed the line from being informative to being annoying a long time ago.That seems to be a sticking point. If they are not in phase then they can't be single phase.