70E say if a 208/120 vac is fed with 125KVA or below a arc flash study is not needed.
Is it correct to assume a hazard risk catagory or 0.
Are there any calculations that would justify this assumption?
Actually the TIA for removal of this note was voted down. The exception will be re-evaluated as part of the 2012 'update' cycle.That note is being removed from the 70E, but as of now it is still valid. It just means you do not need to do a study, it does not mean there is not a hazard. You should defer to the HRC's from the tables.
Actually the TIA for removal of this note was voted down. The exception will be re-evaluated as part of the 2012 'update' cycle.
.
70E say if a 208/120 vac is fed with 125KVA or below a arc flash study is not needed.
Is it correct to assume a hazard risk catagory or 0.
Are there any calculations that would justify this assumption?
We don't even use risk catergory 0 when there's no arc flash calc required. Main hazard becomes shock. We call-out voltage rated gloves and voltage rated tools.
Found this doing a search, does this have any validity?
http://www.bnl.gov/esh/esc/PDFs/Use of Voltage-Rated Gloves - 120V Single Ph. Circuits.pdf
Having no study required does not mean there is not a hazard. Gross misunderstanding of the 70E by your safety people.
I think it would be more helpful if you would define what hazard exist. I don't think anybody says hazard does not exist, but what is it?
We were trying to use our standard Arc Flash sticker and those labels have a section for cal/cm^2. I don't want to leave it blank, and I don't want to buy a seperate sticker for 208/120v panels? Would N/A suffice for the cal/cm^2?
The more I read the more confused I get. So in the case of a 120v lighting panel fed from a 25 kva xfmr would the label say Hazard/Risk catagory 0 based on our standard text "when the covers removed", however if I look at 130.7(C)(9) I think I need to have a risk catagory of 1 for voltage testing, shoot why have the covers off a energized panel if your not taking a current or voltage measurment...ok...I/R scanning? In order to keep the electrical guys safe do we default to the higher level?
I did the calcs (thank to the link you provided) and came up with approx. 1.2 cal/cm^2, hazard cat 0 correct? Since the calcs say it a cat 0 does that supercede the table?