Hi All.  I'm new to the forum here.  I'm studying electrical engineering and having a hard time understanding the 120/240V high leg delta calculations and hoping the senior members here can help.  I have the following loads below:
240 3 phase motor loads total = 38 kva
240 1 phase kitchen loads total = 21 kva
120 1 phase lighting loads total = 9 kva
120 1 phase kitchen loads total = 14 kva
120 1 phase general receptacle loads total = 9 kva
B is the stinger leg.
I've calculated the maximum feeder load to be 194 amps applying 1.25% for lighting continuous loads, and 65% for the kitchen load. Not sure if I did this correctly? Can a member please help?
	
		
			
		
		
	
				