Hfalz1
Member
- Location
- Houston, Tx.
- Occupation
- Electrician
I'm looking at a meter for an office building and the meter says 120/480v what type of service is this? I'm used to 120/240V only.
Can i get 120/240 out or this type of service?
Can i get 120/240 out or this type of service?
A volt meter will tell you what you have.Can i get 120/240 out or this type of service?
You cannot tell anything about the service from looking at those numbers on the meter.Can i get 120/240 out or this type of service?
My guess it it is a high leg delta system, with minimal load on the high leg. You can reduce the size of that conductor - if you provide proper overcurrent protection. Circuit breaker with different rating for one pole then the others would be extremely rare, but you can put different fuses in a fused switch, even use fuse reducers if necessary.Id be interested in the B phase measurement to ground. Maybe nothing but fishy that its a different size..
Sent from my SM-N900P using Tapatalk
It sounds weird to me because the smaller wire on one phase implies a 240/208/120V high leg system, but the red-black-blue color scheme usually means 208/120V wye.My guess it it is a high leg delta system, with minimal load on the high leg. You can reduce the size of that conductor - if you provide proper overcurrent protection. Circuit breaker with different rating for one pole then the others would be extremely rare, but you can put different fuses in a fused switch, even use fuse reducers if necessary.
Red once was common marking on high leg.It sounds weird to me because the smaller wire on one phase implies a 240/208/120V high leg system, but the red-black-blue color scheme usually means 208/120V wye.
Only a voltage check will show for sure, but red-blue-black means 208/120 wye around here.Red once was common marking on high leg.
If it's 208/120 wye, you cannot get 240V from it. Phase to ground would be 120V but phase to phase would only be 208V.Can i get 120/240 out or this type of service?
Typical on older installs here would be red marking on high leg, and no marking on other lines, including white on the grounded conductor. No need to mark it, it lands on the grounded conductor bus because it is the grounded conductor, right?Only a voltage check will show for sure, but red-blue-black means 208/120 wye around here.
Typical on older installs here would be red marking on high leg...