1 There's two connections in series. The code may not state it explicitly, but when there's connections in series it makes sense to consider them separately each in their own context.
2 Often required by utilities, but not by the NEC. Another thing to make sure is okay with the local people who have authority.
3 With that said, I'm with PV farmer
4 A connection to a subpanel to a main with OCPD anywhere between it (the sub) and the service conductors is a load side connection, irrespective of which side of the main breaker (if there is one) on the sub you land your conductors.
1- Ok, but doesn't it also make sense that...yes, you have 2 sets of conductors, each set going to a 100A breaker, and they will carry at most 100A to loads (or 62.5A of PV the other direction)...but!...there is 200A at the lugs below the 200A breaker.
So while the 200A is splitting in 2 directions, those 100A rated conductors are exposed to 200A at the lugs.
I'd go with 200A rated (for the ~6 feet) between lugs and switch, and lugs/house.
2- If it's the difference between a 200 foot run of 300kcmil or 2AWG... why not exceed the requirements?
3- Hey! That's a good thing.
4- Right. However, the 120% rule has nothing to do with conductors.
The OP's setup is different, because the PV is at the opposite end of the busbar from the 100A breaker in the barn, and also at the opposite end of the feeder from the primary source OCD, but isn't the inverter output connection *also* at the primary source OCD end of the feeder for the house?
(2)(1) "that portion of feeder on the load side of the inverter" is going to the house.
(2)(2) the inverter output connection is also the feeder to the barn, and it's tapped to the house feeder.
(2) Bus or Conductor Ampere Rating.
One hundred twenty-five percent of the inverter output circuit current
shall be used in ampacity calculations for the folIowing:
(1) Feeders. Where the inverter output connection is made
to a feeder at a location
other than the opposite end of
the feeder from the primary source overcurrent device,
that portion of the feeder on the load side of the inverter
output connection shall be protected by one of
the following:
(a) The feeder ampacity shall be not less than the sum
of the primary source overcurrent device and
125 percent of the inverter output circuit current.
(b) An overcurrent device on the load side of the inverter
connection shall be rated not greater than the
ampacity of the feeder.
(2) Taps.ln systems
where inverter output connections are
made at feeders, any taps shall be sized based on the
sum of 125 percent of the inverter(s) output circuit
current and the rating of the overcurrent device protecting
the feeder conductors as calculated in 240.21 (B).
(3) Busbars. (nothing about conductors)