A
a.wayne3@verizon.net
Guest
CM called me yesterday an inspection friday was tagged on final oversized breaker on 3.6 kw wall oven.Trim man called me and I told him to use a 25 amp 2 pole.Since 3.6 kw calculates out to 18.75 amps.At 80% that requires a 25 not a 20 he wrote should be there.I`ve never figured a wall oven/cooktop to fall under 3 hour continious usage rule that would allow a 20 amp breaker 