Mgarf33
Member
- Location
- Virginia Beach, Va
Bedroom addition was wired all receptacles with 12awg Romex, picking up lighting ran on 14awg Romex. Inspector disallowed this combination due to the fact that some happy homeowner may come in and change the 15A breaker to a 20A seeing the 12awg wire in the panel. He stated this was also a code violation, but I cannot find this code.
Obviously NM-B is rated at 60°C, but being all on a 15A breaker should be fine. Why is it my responsibility what happy homeowner does without hiring a qualified person to investigate all circuits before deciding to upgrade a breaker. I've never upgraded a breaker guessing that the wires are continuous in one size. Not to mention most receptacles are likely 15A rated anyway.
Obviously NM-B is rated at 60°C, but being all on a 15A breaker should be fine. Why is it my responsibility what happy homeowner does without hiring a qualified person to investigate all circuits before deciding to upgrade a breaker. I've never upgraded a breaker guessing that the wires are continuous in one size. Not to mention most receptacles are likely 15A rated anyway.