I would consider pigtailing the #12 to #14 in the panel. Not saying I would do it, but I would consider it
The inspector is.....okay I'll be nice, mistaken. Saying you cannot have #12 conductors on a 15 amp OCPD leads me to believe that obviously this person doesn't know anything about voltage drop compensation.
I always do that.I would consider pigtailing the #12 to #14 in the panel. Not saying I would do it, but I would consider it
Now you violated a common shirt pocket rule of no splices allowed in a panel.I would consider pigtailing the #12 to #14 in the panel. Not saying I would do it, but I would consider it
Find out who enforces the Virginia adopted the International energy Conservation Code and section C405.9, up-sizing for voltage drop is a new law . I'll add I doubt electrical inspectors know too enforce it yet.Contacted the city again this morning to speak to the electrical supervisor. He's basically backing the inspector stating that if someone were to replace the breaker in the future... blah blah blah, so this must be the city's rule not just the individual inspector. This philosophy is broken, what is to be done with a new high efficiency HVAC unit that has 6awg and the new unit takes a max OCPD of 30? So, happy homeowner replaces a tripping breaker not knowing the compressor has a partially shorted stator. He upsizes the breaker according to conductor size and blows the terminal head straight out of the compressor.
Just plain ignorance is all it is, I guess we need to replace the conductor whenever we upgrade the appliance efficiency? They can simply hide behind the "wiring methods" deemed safe practice by the AHJ for anything the dream up. A contractors only fight is to file an appeal holding up a job for potentially a month. Ridiculous! There's got to be a better way to fight this kind of abuse. I mean hell, criminals become hero's in our country, so why are tradesmen left to suffer with governmental incompetence?
Seems that likely would be something that actually needs to go into lawbooks as a start to get EI's enforcing it? Not saying this code isn't in lawbooks, but might not be noted in the electrical division's (or whatever they may call it) duties of enforcement. Here about only code mentioned for EI's to enforce is whichever edition of NFPA 70 they have on file and some other local rules (which are mostly licensing and permit rules and such) and that is about it. So if it is not something addressed in NEC, they don't have much say in what you can or can't do.Find out who enforces the Virginia adopted the International energy Conservation Code and section C405.9, up-sizing for voltage drop is a new law . I'll add I doubt electrical inspectors know too enforce it yet.
so this must be the city's rule not just the individual inspector. This philosophy is broken,
If it's the city's rule, the inspector can point you to a written amendment. Otherwise it's his own imagination and he should be challenged on it....so this must be the city's rule not just the individual inspector....
Yeah the way it happens here is the building inspectors / plans reviewers enforce the other codes that impact electrical installations. Its the same energy code that requires me to do a lighting energy code calc before we do new commercial work.Seems that likely would be something that actually needs to go into lawbooks as a start to get EI's enforcing it? Not saying this code isn't in lawbooks, but might not be noted in the electrical division's (or whatever they may call it) duties of enforcement. Here about only code mentioned for EI's to enforce is whichever edition of NFPA 70 they have on file and some other local rules (which are mostly licensing and permit rules and such) and that is about it. So if it is not something addressed in NEC, they don't have much say in what you can or can't do.
Yes there may be other inspectors and not just EI's that can impact what we do. I mostly have to just deal with EI's where I am. Sometimes fire marshal, though that usually is over when/where certain items must be present and not so much on how they are installed. Egress lighting maybe the number one thing there. Commercial cooking exhaust hoods maybe next. They don't care how you wire the hoods, That is for the EI, just that it shuts off the appliances when actuated and turns the exhaust fan on even if it wasn't already on.Yeah the way it happens here is the building inspectors / plans reviewers enforce the other codes that impact electrical installations. Its the same energy code that requires me to do a lighting energy code calc before we do new commercial work.
There are lots of other things in codes that impact our work, like structural codes that regulate how big a hole you can drill thru a stud, fire codes that say where smoke detectors go in a dwelling, mechanical code says bath fan has to be on a timer or some automatic device etc etc.
If you say wire a new house here and don't wire for hard wired smokes you'll pass your rough electric inspection but fail a building building inspection.
What do you mean? It will end up on 20 amp circuits like everything else and occasionally even on 30 amp circuits.Just wail till we get copper clad #14 aluminum and 10 amp branch circuits next year, I bet the average handyman / home owner will not be able to distinguish it from regular 14 and lots of it will end up on 15A circuits.
Yes, that was a sad story, the first victim was a contractor filling out paperwork in his vehicle. He proceeded to go in and shoot a bunch of co-workers. I live about 2 miles away from this location. I had been there on many occasions, but mostly file permits online these days. They demolished the huge building and relocated the inspections department several miles away.Hmmm, tread lightly there, just saying, this happened:
Your inspector is an idiot, there is a pretty picture exhibit 220.4…10 on 15 amp and 13 on 20 amp but this is commercial and industrial, the NEC has no limit for receptacles in a residential structure.Contacted the city again this morning to speak to the electrical supervisor. He's basically backing the inspector stating that if someone were to replace the breaker in the future... blah blah blah, so this must be the city's rule not just the individual inspector. This philosophy is broken, what is to be done with a new high efficiency HVAC unit that has 6awg and the new unit takes a max OCPD of 30? So, happy homeowner replaces a tripping breaker not knowing the compressor has a partially shorted stator. He upsizes the breaker according to conductor size and blows the terminal head straight out of the compressor.
Just plain ignorance is all it is, I guess we need to replace the conductor whenever we upgrade the appliance efficiency? They can simply hide behind the "wiring methods" deemed safe practice by the AHJ for anything the dream up. A contractors only fight is to file an appeal holding up a job for potentially a month. Ridiculous! There's got to be a better way to fight this kind of abuse. I mean hell, criminals become hero's in our country, so why are tradesmen left to suffer with governmental incompetence?