Not following you: Feeder supplies two motors of 40A FLC, nothing else. 430.24 says the conductors must have 90A ampacity. 430.62(A) says the OCPD may be up to 140A, so lets use 125A. The 125A OCPD provides SC/GF protection. The two downstream motor overloads provide overload protection. Protection is split.As I explained thats not the way I interpret it, but it will be interesting to see what happens with your PI, I think we all agree it could be more clearly addressed.
Cheers, Wayne