We do not need anything in G telling us we can ignore D as D has already told us we can ignore D if the application is covered by G.
My thoughts exactly
We do not need anything in G telling us we can ignore D as D has already told us we can ignore D if the application is covered by G.
I did - and over, and over again I come to the same conclusion.It seems your the only one that has an issue with this section, when that happens to me I try to re-think my position.![]()
I did - and over, and over again I come to the same conclusion.
Please point to someplace in the codes listed in 240.4(G) that "specifically permits" 240.4(D) to be not applicable.... Or refute in some way that "A through G" means ONLY "G"........
We do not need anything in G telling us we can ignore D as D has already told us we can ignore D if the application is covered by G.
It does say (E) or (G), and 240.4(E)(2) specifically permits fixture wire to be installed in accordance with 240.5(B)(2).. . .Please point to someplace in the codes listed in 240.4(G) that "specifically permits" 240.4(D) to be not applicable.... Or refute in some way that "A through G" means ONLY "G"....
250.122 says (2008) that "in no case shall they (EGC's) be required to be larger than the circuit conductors supplying the equipment.Anyway - so what do you think of 250.122? IMO that pretty much backs it up, as 20A would require a min of #12, and 30A would need a min of #10 for a EGC - pretty hard to do other than that with cable... Putting it in line with 240.4(D) - AGAIN....
Anyway - so what do you think of 250.122? IMO that pretty much backs it up, as 20A would require a min of #12, and 30A would need a min of #10 for a EGC - pretty hard to do other than that with cable... Putting it in line with 240.4(D) - AGAIN....
the egc does not have to be larger than the circuit conductors, sorry can't remember which section says that.![]()
Man, I really wish the forum software would quit changing upper-case letters to lower case.
I did - and over, and over again I come to the same conclusion.
Please point to someplace in the codes listed in 240.4(G) that "specifically permits" 240.4(D) to be not applicable.... Or refute in some way that "A through G" means ONLY "G"....
Anyway - so what do you think of 250.122? IMO that pretty much backs it up, as 20A would require a min of #12, and 30A would need a min of #10 for a EGC - pretty hard to do other than that with cable... Putting it in line with 240.4(D) - AGAIN....
I agree, sometimes it is a pain.
It does say (E) or (G), and 240.4(E)(2) specifically permits fixture wire to be installed in accordance with 240.5(B)(2).
240.5(B)(2)(2) allows fixture wire of 14 AWG to be tapped to a 20-ampere circuit.
250.122 says (2008) that "in no case shall they (EGC's) be required to be larger than the circuit conductors supplying the equipment.
#14 to lighting on a 20 a circuit can be compliant.![]()
What we can do for you is to take a 3 pound hammer, with a nice soft rubber covering and just give you a very nice club to the forehead...I believe it will not only help, but will not leave much evidence behind.![]()
Sure you can choose to find something in 240.4(E) or (G) to get out of (D) - but what in those codes listed in each (E) or (G) "Specifically Permits" the contradiction of allowing higher amperages on smaller conductors that would otherwise be limited. Without a "specific" perimission IMO you are stuck with 240.4(D) on small conductors #10 or smaller.Here's my take:
240.4(D) says you get to choose:
~~~~
If my application doesn't fall under (E), (F) or (G), then I'm stuck with 240.4(D)(1) through (7).
Sure you can choose to find something in 240.4(E) or (G) to get out of (D) - but what in those codes listed in each (E) or (G) "Specifically Permits" the contradiction of allowing higher amperages on smaller conductors that would otherwise be limited.
Without a "specific" permission IMO you are stuck with 240.4(D) on small conductors #10 or smaller.
Can anyone point to any language in any of the codes listed in (E) or (G) that says '240.4(D) shall not apply'? That would be "specific"...
That's not true. The allowable ampacity of #14 fixture wire is 17 amps. As my first post stated, 402.10 allows fixture wire to be used "for connecting luminaires to the branch-circuit conductors supplying the luminaires." I could run 50 feet of #18 fixture wire if I wanted to (I don't want to, but I can). 240.5(B)(2)(1).But not as a switch leg, normallly designed, configured, and installed. Your reference only applies to fixture wire, which by definition is that wire installed within a given fixture or its attachment whip, not the switched branch circuit wiring which feeds the box from which the fixture is fed.
Show me.The difference is a fixture whip is exposed and not allowed to be concealed behind the building finish, the #14 switch leg is, which would require a 15 amp OCPD max
notice all the wiring methods in 240.5 have this (exposed) requirement elsewhere in the code
Fixture wire is not a wiring method. Where between the outlet and fixture do you propose concealing the wire beneath the building finish?That's not true. The allowable ampacity of #14 fixture wire is 17 amps. As my first post stated, 402.10 allows fixture wire to be used "for connecting luminaires to the branch-circuit conductors supplying the luminaires." I could run 50 feet of #18 fixture wire if I wanted to (I don't want to, but I can). 240.5(B)(2)(1).
Show me.
Not talking about fixture whips anyway, only fixture wire. Nothing in Article 402 requires the method to be exposed.
400.8 Uses Not Permitted. Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(1) As a substitute for the fixed wiring of a structure
(2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces Exception to (4): Flexible cord and cable shall be permitted to be attached to building surfaces in accordance with the provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
(6) Where installed in raceways, except as otherwise permitted in this Code
(7) Where subject to physical damage
400.7 Uses Permitted.
(A) Uses. Flexible cords and cables shall be used only for the following:
(1) Pendants
(2) Wiring of luminaires
(3) Connection of portable luminaires, portable and mobile signs, or appliances
(4) Elevator cables
(5) Wiring of cranes and hoists
(6) Connection of utilization equipment to facilitate frequent interchange
(7) Prevention of the transmission of noise or vibration
(8) Appliances where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connection
(9) Connection of moving parts
(10) Where specifically permitted elsewhere in this Code
It seems that the disagreement is just about the word "specific". For most readers, a line item entry in Table 240.4(G) is sufficiently "specific" to satisfy 240.4(D)'s clause "Unless specifically permitted in 240.4(E) or (G)". That is, we read the word "specifically" in 240.4(D) to mean a specified conductor application, not an actual sentence saying "foo is exempted from 240.4(D)".Sure you can choose to find something in 240.4(E) or (G) to get out of (D) - but what in those codes listed in each (E) or (G) "Specifically Permits" the contradiction of allowing higher amperages on smaller conductors that would otherwise be limited. Without a "specific" perimission IMO you are stuck with 240.4(D) on small conductors #10 or smaller.
Everybody knows that foo is exempted...that goes without saying. :grin:It seems that the disagreement is just about the word "specific". For most readers, a line item entry in Table 240.4(G) is sufficiently "specific" to satisfy 240.4(D)'s clause "Unless specifically permitted in 240.4(E) or (G)". That is, we read the word "specifically" in 240.4(D) to mean a specified conductor application, not an actual sentence saying "foo is exempted from 240.4(D)".
Cheers, Wayne