Volta, Convincing post, and at times I have wondered myself, however, the "point on the wiring system" is the outlet (or fixture) itself and, IMHO, the conductors to that point would be branch circuit conductors and 402.11 Uses Not Permitted.
Fixture wires shall not be used as branch-circuit conductors except as permitted elsewhere in the Code.
But, admittingly, thats MY point of view, but I think it is also supported by the fact that the conductors listed in 402 all have the "application provision" fixture wiring". Some additional Code clarification might be in order.
One common installation of an "outlet" located away from the "utilization" equipment is that required by
210.11 > 220.10 > 220.12 > 220.12(F) > 600.5(A) > "accessible location at each entrance to each tenant space for sign or outline-lighting use . . .".
So this is often located as a junction box in an attic, above a ACT ceiling, on a wall surface, etc. The sign contractor typically extends a FMLC whip or similar from the exterior sign to the interior outlet.
The sign is not the outlet, the 4-square in the attic is.