So 406.4(D)(2) allows replacement of non-grounding receptacles with a GFCI receptacle, and that GFCI can supply other grounding-type receptacles as long as they're marked "GFCI Protected" and "No Equipment Ground".
And 250.114 requires many types of residential cord and plug connected equipment to be connected to an equipment grounding conductor.
What would be the point of that? Doesn't a GFCI without an EGC provide an equivalent level of personnel protection to a grounded type receptacle with an EGC? If a homeowner can plug in other cord and plug connected equipment (not listed in 250.114(3)), why would that equipment be safe to use? How would a homeowner reasonably be expected to understand that distinction?