1st. house wired.....

Status
Not open for further replies.

MRI

Member
Hi everyone. I have been reading through posts on here for some time now and have learned a lot about the pains of starting a new business and working for yourself. I have been a industrial plant electrician for 20 years now and I am trying to branch off on my own...some residential and light commercial. Anyway, I wired my first home and had it inspected today. It failed for one fan box not grounded and I had the stove hood fan ran off one of the two small appliance ckts. I knew this had to be changed but forgot to before the insp got there. Not to bad for my first house I guess. My question is do most of you just wire the hood fan into a the kitchen lighting ckt. or even a general lighting ckt.? I don't think a dedicated ckt is needed.....

Thanks for taking the time to read this......
 
MRI said:
. . . and I had the stove hood fan ran off one of the two small appliance ckts.
Was it a gas stove? If so, this would have been acceptacle, per Exception 2 to 210.52(B)(2). Otherwise, it could be on a lighting circuit, provided the circuit had capacity for the load. I see no reason for it to be on a dedicated circuit.

Welcome to the forum.
 
Yes, its a hard wired connection. I'll change it to a lighting circuit and call in another inspection for tomorrow. Thanks for the help.
 
jimport said:
If this was a cord and plug connected range hood it would require a dedicated circuit. If it was hardwired it could be on the general lighting circuit.
Before I posted my earlier comment, I took a quick look through the code, and couldn't find that requirement, and had to go back to work (sigh :roll:) . Can you give me a reference article?
 
MRI said:
Hi everyone. I have been reading through posts on here for some time now and have learned a lot about the pains of starting a new business and working for yourself. I have been a industrial plant electrician for 20 years now and I am trying to branch off on my own...some residential and light commercial. Anyway, I wired my first home and had it inspected today. It failed for one fan box not grounded and I had the stove hood fan ran off one of the two small appliance ckts. I knew this had to be changed but forgot to before the insp got there. Not to bad for my first house I guess. My question is do most of you just wire the hood fan into a the kitchen lighting ckt. or even a general lighting ckt.? I don't think a dedicated ckt is needed.....

Thanks for taking the time to read this......

It sounds like you may be considering leaving your Industrial maintenance job for your own business....Is that right.
 
charlie b said:

Before I posted my earlier comment, I took a quick look through the code, and couldn't find that requirement, and had to go back to work (sigh :roll:) . Can you give me a reference article?

I believe he is refering to 422.16(B)(4)
 
charlie b said:

Was it a gas stove? If so, this would have been acceptacle, per Exception 2 to 210.52(B)(2).

I think because it is a gas cook top that this exception covers me....I will wire it to a gen. ltg. ckt. and not argue the small stuff with the AHJ on my first insp.
 
mdshunk said:
That was a pretty sharp inspector who caught one fan box not grounded. Either that, or you ticked him off somehow. :grin:

Around here, once the inspector "knows who you are" then he doesn't check much of anything.
 
peter d said:
Around here, once the inspector "knows who you are" then he doesn't check much of anything.
I think that's pretty much true everywhere. Unless I'm doing something sufficiently weird, I really don't get checked out very well, and that's a shame. I really appreciate a good once-over. I'd actually welcome a righteous red tag every once in a while. It's part of learning.
 
Well I'm sure since the inspector hasn't seen my work before he was going to be looking a little closer until he knows me a little more, it happens in every aspect of the industry. As far as the hood fan, he really had no way of knowing it was going to be gas. Maybe I should have tagged the wire so he would have known???? No one was on the job when he walked through. The ceiling fan box was in a 14' tall ceiling in the family room....how he noticed it wasn't grounded......I don't know.
 