I agree with the others, run a 12/3. If it's single phase why were you concerned about a MWBC?
Ok this is something new to me. I now can understand this concept, however, what dereckbc said makes it sound like you will only reduce the voltage drop if you use the shared neutral on single phase. I don't see how this would make any difference. Another words this concept should also work on 3 phase just the same.
If you run two hots and two neutrals from the panel to the loads you have 4xLength in conductors. If you run a MWBC, you have only three, so your voltage drop is limited to 3xLength in conductors.
Step up to three phase, and if you run 3 hots and 3 noodles, you have 6xLength, but with a MWBC, you only have 4xLength.
.
The diagram Bob posted makes no reference to single- or three-phase. The voltage drop would be the same.
I don't think length is the story, load is. Look at the load on the neutral in Ed's diagrams.
I agree with the others, run a 12/3. If it's single phase why were you concerned about a MWBC?
It's not the whole story. Just half of it. Instead of I of both loads being run over two seperate wires, the difference between them is run over only one.
why would he be concerned if it were 3 phase instead of single phase? Am I missing something here? Is it not acceptable to run 12-3 and share the neutral if it were a 3 phase panel? Wouldn't the 2 circuits still cancel each other out on the neutral assuming they are identical loads.
Don't know why I'm asking. I know the answer to be yes. It shouldn't matter if he's on 1 or 3 phase. As long as the 2 circuits are on seperate legs then they are subtractive, not additive.
why would he be concerned if it were 3 phase instead of single phase?
We will remain in disagreement on this one, when you calculate the voltage drop you will use the 2x the circuit length, not 3x, 4x or 6x.
I don't think we're disagreeing, Bob. We're just using a different angle of attack on the same problem.
I'm using field artillery, and you've mounted an air strike. Taget eliminated just the same.
Only thing wrong with the diagram is that in the shared neutral version the arrows for the direction of flow are the wrong direction for the neutral and the 60 amp circuit.
I actually agree with 480 on this one. It does have to do with the one fewer conductor or neutral, but I can see your outlook on it as well. They are inverse opinions of each other. Both being cause and effect on one another. You can't have one without the other.I think your field artillery is firing blanks.
I think your field artillery is firing blanks.
I actually agree with 480 on this one. It does have to do with the one fewer conductor or neutral,
the 2 circuits should be pointing out and the neutral pinting back to source or opposite the outgoing hots.Actually if the circuit was DC it is drawn correctly.
If it's AC then the arrows should point both ways or not even be there.
480 just didn a pretty good job of it himself right above your post.Would you care to prove that with a voltage drop calculation?
If you still say we disagree, then I'd say your planes are grounded instead. :grin:
Would you care to prove that with a voltage drop calculation?