I still can't wrap my head around why it would be acceptable to combine 3 devices such that
B series rate with A
and C series rate with A
I mean, why are we not including B being series rated with C?
assuming 200kAIC, 65kAIC, 22kAIC respectfully.
I'm just still extremely baffled by this quote from Eaton "Breakers A, B, and C are in series respectively from main to branch. Breakers A and B series rate together. Breakers A and C series rate at the same interrupting level (or higher). It is allowable to use A, B, and C together at the A-B series rating"
Why is Eaton the only one saying this? This is suspicious to me.
I found a quote from a comment you had a long time ago:
https://forums.mikeholt.com/threads/three-100-amp-panels.2551448/
you said "Another option is to rate A-B and A-C as long as A-C has the same (or higher) interrupting level as A-B."
Can you give me an example? I'm seriously desperate to figure this out lol