2 fuses and branch breakers series rating
If D is the only thing that is not fully rated, then either A, B or C must be series rated with D for this to be ok.
E and F don't matter since they are fully rated downstream of D.
But that brings up more questions... from previous conversations and Eaton's option 4
Is it acceptable to use A, B, C, D, E, F in series in this scenario?:
B rate with A, C rate with A, D rate with A, E rate with A, and F rate with A
B, C, D, E, F don't rate with each other
Well that's just the infamous option 4 we have been discussing the last several dozen posts isn't it? I would say based on the Eaton document it is perfectly fine.
Well that's just the option 4 we have been discussing the last several dozen posts isn't it? I would say based on the Eaton document it is perfectly fine.
The only difference is they used 3 different overcurrent protections, that's why I brought it up.
Going to just stop you there because I have an issue with "is sufficient for the AFC at D". I don't really know what that means.
If you like, C has an AIC rating, D has an AIC rating, and then if (C,D) is series rated, D gets a "joint" AIC rating when used with C just upstream. I gather that usually that joint AIC rating is the AIC rating of C, and you just say C and D are series rated, but there's no particular reason the joint AIC rating has to match C's AIC rating. So all I was saying for my example is that the joint rating for (C,D) is greater than the AFC at D.
Cheers, Wayne