Is connected properly for three phase four wire with high leg, but I didn't notice the ground symbol was on the wrong lead first time around.Wrong as is in non-standard (agree), or wrong as in an NEC violation (disagree)?
Cheers, Wayne
Is still three phase four wire with high leg, but does not comply with 250.26 if grounding the lead that is shown grounded.
If only using as three phase three wire (not utilizing either center tap at all besides putting each half of each secondary coil in series with one another) then it becomes corner grounded, in which case you can ground any one of the three leads being utilized as system conductors.