But the right transformer symbol in the original post is a wye-delta transformer, but the left symbol has "|||-wye", and I have no clue what that is.
Typically both transformers would have the same primary side winding configuration. There would be one Wye secondary and the other Delta to provide a 30° phase shift.It gave 12 output pulses per input cycle and required much less filtering to produce a steady DC output.
Typically both transformers would have the same primary side winding configuration. There would be one Wye secondary and the other Delta to provide a 30° phase shift.
If it is wired wierd then you wont have a clean phase shift between them.Yes, I'd expect that the first transformer to be a wye-wye and wye-delta.
Maybe @Jraef will chime in, if the '|||-wye' transformer is a weird but real thing, or if it looks like a typo.
IEC 60076-1:I agree with @jim dungar that this is a VFD front end with different transformer phasing. The square blocks with ~/= are pretty common for AC/DC conversion (rectification) and =/~ for DC to AC conversion (inversion). The diagram is pretty clear about two _different_ transformers feeding two different AC/DC blocks feeding a common DC bus.
What I am not familiar with is the transformer symbol with three parallel lines. A typical '12 pulse' rectifier starts with a delta-wye and a delta-delta transformer prior to the two rectifier blocks. But the right transformer symbol in the original post is a wye-delta transformer, but the left symbol has "|||-wye", and I have no clue what that is.
I _think_ the triangles/arrows on the single lines are cable connections, but also not sure on that.
-Jonathan
EC 60076-1:If it is wired wierd then you wont have a clean phase shift between them.
I have never seen a 3 phase transformer primary other than Wye, Delta, or T.

IEC 60076-1:
Open windings in a three-phase transformer (that are not connected together in the transformer but have both ends of each phase winding brought out to terminals, for example the line windings of series and phase-shifting transformers) are indicated as III (HV), or iii(intermediate or low-voltage windings).
That's like 13,500 horsepower if that KW figure is mechanical. What's the black box on the side with the dashed line? Is this some kind of synchronous AC machine?
Yeah, it's got to be, or maybe something like a synchronous condenser for stabilization?My guess was an exciter for some sort of synchronous machine. It's fed from circuit T5 via AC/DC conversion. Synchronous generator in some sort of variable speed service, with a DC link to supply grid frequency?


Why would that be on the primary side? I would think it would be on the secondary side.IEC 60076-1:
Open windings in a three-phase transformer (that are not connected together in the transformer but have both ends of each phase winding brought out to terminals, for examplethe line windings of series and phase-shifting transformers) are indicated as III (HV), or iii(intermediate or low-voltage windings).
Yes arrows are cable interconnection between both primaries.
I dont get how that works on the primary side, do you mean like a zig-zag configuration? I could see it on the secondary side.The left primary is a '6 bushing' transformer and each of the three phase coils is connected _in series_ to the respective right primary phase.

A zig-zag would not provide the two isolated outputs shown in the OP.I dont get how that works on the primary side, do you mean like a zig-zag configuration? I could see it on the secondary side.
Connecting two sets of coils in series would mean you have voltage drops across each one. Each winding would never see the full L-N voltages.So you essentially have the two primary windings electrically in series.
IMHO 'AI' got that one very wrong. The three lines shown are not _between_ the primary and secondary. They represent the primary.
An electrostatic shield might show up as 3 lines if it is paired with the symbol for the core, eg:
View attachment 2581477
OP described the meaning of the 3 lines in post #8. The 3 parallel lines are the symbol for a primary that is neither wye or delta, but instead has all 6 terminations brought out. The primary could be connected wye or delta with suitable external jumpers, or it could be used in some other fashion.
-Jonathan
I thought about zig zag also, but why?zig-zag configuration?
Connecting two sets of coils in series would mean you have voltage drops across each one. Each winding would never see the full L-N voltages.
I wonder if this is simply a reconnectable transformer that would allow the installer to create additive or subtractive connections resulting in a positive or negative 30° phase shift on the output compared to the delta output on the other transformer?