20 amp circuits

Status
Not open for further replies.

Casselectric

Member
Location
Ct
On 20 amp circuits can 20 amp receptacles be used if dedicated circuit. Inspector telling me can't put multiple 20 amp devices on one circuit.? This allows for more then one 20 amp appliance to be used.
 
Yes
kitchen circuit Installed 20 amp receptacles, inspector is stating 20 amp receptacles should only be used if branch circuit is dedicated for that only device.
 
Yes
kitchen circuit Installed 20 amp receptacles, inspector is stating 20 amp receptacles should only be used if branch circuit is dedicated for that only device.

You cannot use 20A receptacles on a 15A circuit.
You can use 15 or 20A receptacles on a 20A circuit, unless there is only one receptacle, then it must be a 20A. One receptacle meaning a simplex (single outlet). You can run a single 15A duplex outlet on a 20A circuit.

Sounds like the inspector is misreading, misremembering or misquoting 210.21(B)(1)
 
You cannot use 20A receptacles on a 15A circuit.
You can use 15 or 20A receptacles on a 20A circuit, unless there is only one receptacle, then it must be a 20A. One receptacle meaning a simplex (single outlet). You can run a single 15A duplex outlet on a 20A circuit.

Sounds like the inspector is misreading, misremembering or misquoting 210.21(B)(1)
I agree with you and others that the inspector is wrong.

Just for clarity- You cannot use 20A duplex receptacles on a 15A circuit....
You can use 15 or 20A duplex receptacles on a 20A circuit....
 
I would add that you could use a 20 amp single receptacle on a 15 amp circuit if it's the only receptacle. Regarding the OP and the kitchen receptacles the inspector is incorrect.
 
On 20 amp circuits can 20 amp receptacles be used if dedicated circuit. Inspector telling me can't put multiple 20 amp devices on one circuit.? This allows for more then one 20 amp appliance to be used.

Yes
kitchen circuit Installed 20 amp receptacles, inspector is stating 20 amp receptacles should only be used if branch circuit is dedicated for that only device.

I would think the inspector is just confused. Probably not an electrical inspector but multi-trade type.

At one time a lot of electricians thought that on a 20 amp circuit that you had to use 20 amp receptacles. You will see a lot of 20 amp receptacles used in older kitchens.

In residential you are not going to see many appliances with a 20 amp plug, I don't think I have ever seen any.

No reason you can't use then except it's a waste of money in residential.
 
On 20 amp circuits can 20 amp receptacles be used if dedicated circuit. Inspector telling me can't put multiple 20 amp devices on one circuit.? This allows for more then one 20 amp appliance to be used.

Dedicated to what?

Yes
kitchen circuit Installed 20 amp receptacles, inspector is stating 20 amp receptacles should only be used if branch circuit is dedicated for that only device.

Is this a commercial kitchen?
Is it for a listed appliance where the listing requires a dedicated circuit?

Just trying to figure out what's going on. It's the internet, ya know.
 
On 20 amp circuits can 20 amp receptacles be used if ​dedicated circuit. Inspector telling me can't put multiple 20 amp devices on one circuit.? This allows for more then one 20 amp appliance to be used.

Dedicated to what?



Is this a commercial kitchen?
Is it for a listed appliance where the listing requires a dedicated circuit?

Just trying to figure out what's going on. It's the internet, ya know.

I agree- Surely the inspector cannot be that idiotic to limit the number of 20a devices on gen/sabc 20a ckts-the op did say dedicated.

Maybe he means that the inspector wont let him use a duplex on a dedicated ckt serving single appliance-(answer to that by JFletcher in post #5). Maybe op will provide more details.
 
Last edited:
To add to (or perhaps to detract from) the clarity of this issue, let me point out (as others have danced around) the fact that the concept of "dedicated circuit" does not appear in the code. There exist an animal called "individual branch circuit," and some people (incorrectly) use the phrase "dedicated circuit" as though it meant the same time. Given that "dedicated circuit" does not have an NEC definition, it won't mean the same thing to everyone who uses (or hears, or reads) that phrase.
 
On 20 amp circuits can 20 amp receptacles be used if dedicated circuit. Inspector telling me can't put multiple 20 amp devices on one circuit.? This allows for more then one 20 amp appliance to be used.

On a practical level, when dealing with DH inspectors, it is nearly always simpler to just say OK and change it.

Have even 'heard of' electricians installing 20 cent big box TR receptacles in a woodworking shop 'cause AHJ insisted that it could be converted to someplace with kids crawling around someday -- then switching out the TR for spec grade 20A twist lock after write-off. ;)
 
To add to (or perhaps to detract from) the clarity of this issue, let me point out (as others have danced around) the fact that the concept of "dedicated circuit" does not appear in the code. There exist an animal called "individual branch circuit," and some people (incorrectly) use the phrase "dedicated circuit" as though it meant the same time. Given that "dedicated circuit" does not have an NEC definition, it won't mean the same thing to everyone who uses (or hears, or reads) that phrase.

If a listing uses the nomenclature "dedicated circuit" or "dedicated branch circuit" and the installation needs to accommodate the listing, then would you agree that it's proper use of the phrase? And if that's the case, such as a dough mixer (Hobart) in a commercial kitchen, wouldn't the inspector be correct?
 
Are you suggesting that the instructions that came with the listing had that phrase, or that the instructions that came in the box when you bought the item had that phrase? They are not the same thing.
 
Are you suggesting that the instructions that came with the listing had that phrase, or that the instructions that came in the box when you bought the item had that phrase? They are not the same thing.

I'm suggesting the instructions which are part of the listing for the Hobart appliance contained the language.
 
and if that was the case would it have to be a single receptacle & not a duplex??? beware of what you ask for
Can you point to any NEC language that says a cord-and-plug connected load on an individual branch circuit can't be connected via a duplex receptacle?

Sure you could plug something else into the duplex receptacle, but that's just a "what if". If you plug in only one piece of utilization equipment, you still have an individual branch circuit, to my understanding.

Cheers, Wayne
 