There have been a number of proposal to require only an single receptacle outlet on an individual branch circuit. They were all rejected by the Code Making Panel.
if that was the actual ask then its obvious why that was rejected, because a indi-bc is not limited to receptacle terminations.
fix the art-100 def and this issue can likely go away. or, add clarity in every section that talks about the requirement for a indi-bc.
i think fixin art-100 def is easier.
and i believe from nec code, you technically dont need indi-bc under some circumstances, eg; the device is rated no more than 50% of the bc's rated ocpd, something like that. so if you have a fridge that is rated 10A you dont need indi-bc if the bc is 20A, etc. <-- but pls check me on this, i used fridge as example, but perhaps this is limited to perm mounted utility device?
but, is nec trying to enforce all future probabilities (they technically cannot), lets say that 10A fridge (or util device) is replaced with a 15A item, thats ok for the BC but not ok under nec verbiage. i guess this would be a AHJ call.