Is it safe to take a 20 amp outlet, cut the jumper between the two load screws and put two 20amp circuits two that one outlet? I didn't like the idea but a guy I work with said it was fine to do so.
That's from the 2008 NEC. In 2011 it's just Article 210.7 (without the B).210.7(B) Multiple Branch Circuits. Where two or more branch circuits supply devices or equipment on the same yoke, a means to simultaneously disconnect the ungrounded conductors supplying those devices shall be provided at the point at which the branch circuits originate.
It is done all the time with G.D. & D.W. circuits.
Is it safe to take a 20 amp outlet, cut the jumper between the two load screws and put two 20amp circuits two that one outlet? I didn't like the idea but a guy I work with said it was fine to do so.