rubob
Member
- Location
- Asheville North Carolina
I have done an installation in a commercial building with a 400 amp single phase service that is the only service on the building. Inside I used both white and gray for my neutrals thinking it would make it easier to group my neutrals with their ungrounded conductors. I failed inspection because, to his credit, the inspector pointed out to me that 200.6 states that 'An insulated grounded conductor of 6AWG or smaller shall be identified by ONE of...
When you read that section I can't believe that is the intent of the code because there will be situations where you can't have just one of those choices in a building. Should that read ANY or should I start pulling half my neutrals out to replace them with a single color?
I understand that it would be a different situation if there were multiple voltage systems present.
When you read that section I can't believe that is the intent of the code because there will be situations where you can't have just one of those choices in a building. Should that read ANY or should I start pulling half my neutrals out to replace them with a single color?
I understand that it would be a different situation if there were multiple voltage systems present.