Here is a test I wrote a couple of years back.
Note; all scenarios are cable assemblies in normal 120/240 volt single phase residential installations and the white conductor is not re-identified.
Also note that the answers do not not necessarily have to be code compliant, (more than one answer might work too
the questions are dealing with whether an electrician would need the white conductor re-identified to know what it is doing per the scenarios.
Scenario #1 You open a box containing a single pole switch and find a white conductor and a black conductor from the same cable connected to the switch, an Electrician will know the white conductor is _______
(A) a hot conductor or switch leg
(B) an EGC
(C) a Grounded Conductor
(D) a High Leg
Scenario #2 You take a panel cover off and see a 2 conductor cable whose white conductor is connected to one pole of a multi-pole breaker and the black conductor of this cable is connected to the other pole, an Electrician will know this white conductor is being used for a _________
(A) Main Bonding Jumper
(B) GEC
(C) Grounded Conductor
(D) Hot Conductor
Scenario #3 You are trouble shooting a set of three-ways and see a white conductor connected to a terminal on the first switch you open, an Electrician would know this conductor would be a ________
(A) colored conductor that lost its pigment
(B) bleached and enriched wheat conductor
(C) skinny Caucasian guy
(D) traveler or hot conductor
Scenario #4 You open a light fixture box and find a 2 conductor cable whose white conductor is wire nutted to the blacks of the other cables in the box, the black conductor of this cable is connected to the fixture, an electrician would know this white conductor is________
(A) not a Bigot
(B) a Data Cable
(C) a hot conductor
(D) a piece of tie wire
Given the scenarios above, it is necessary to
re-identify a white conductor used as a hot so that __________ will not be confused and spend the rest of the day scratching his/her head.
(A) an Electrician
(B) a fellow Electrician
(C) an Electrician working in FL
(D) a person that should not have their paws in these boxes in the first place.
IMO there is no reason for the requirement. :wink:
Roger