Panel Meeting Action: Accept in Principle
Accept the proposal as modified by revising the proposed exception to read as
follows:
The grounded circuit conductor shall be permitted to be omitted from the
switch enclosure where either of the conditions in (1) or (2) apply:
(1) Conductors for switches controlling lighting loads enter the device box
through a raceway.
(2) Cable assemblies for switches controlling lighting enter the box through a
framing cavity that is open at the top or bottom on the same floor level, or
through a wall, floor, or ceiling that is unfinished on one side.
Panel Statement: This exception should only be applied in cases where
compliance with the normal requirements is so difficult that covert attempts to
evade the rules would be likely.