200.7 Using white wire as ungrounded conductor

Status
Not open for further replies.

flashlight

Senior Member
Location
NY, NY
Occupation
Electrician, semi-retired
One other comment regarding the "spider" system-- having been
inconvenienced by this system 10-15 years ago, when people changed
over to low voltage electronic light fixtures, the dimmer for those required a white (grounded) conductor at the switch box, so since then I would always pull a 12/3 to the switch if the feed landed at the ceiling box. Less common problem now, due to advances in xfmr technology.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
If proposal 9-95 passes the comment stage then a grounded conductor will be required at most switch locations in the 2011 NEC.

9-95 Log #1160 NEC-P09 Final Action: Accept in Principle
(404.2(C) (New) )
_______________________________________________________________
Submitter: Vince Baclawski, National Electrical Manufacturers Association
(NEMA)
Recommendation: Add a new subparagraph 404.2(C) and exception to read as
follows:
404.2 Switch Connections.
(C) Switches Controlling Lighting Loads. Where switches control lighting
loads supplied by a grounded general purpose branch circuit, a grounded circuit
conductor shall be provided at the switch location.
Exception: Grounded conductors shall not be required where conductors for
switches controlling lighting loads enter the device box through a raceway.

The CMP also added this:

Panel Meeting Action: Accept in Principle
Accept the proposal as modified by revising the proposed exception to read as
follows:
The grounded circuit conductor shall be permitted to be omitted from the
switch enclosure where either of the conditions in (1) or (2) apply:
(1) Conductors for switches controlling lighting loads enter the device box
through a raceway.
(2) Cable assemblies for switches controlling lighting enter the box through a
framing cavity that is open at the top or bottom on the same floor level, or
through a wall, floor, or ceiling that is unfinished on one side.
Panel Statement: This exception should only be applied in cases where
compliance with the normal requirements is so difficult that covert attempts to
evade the rules would be likely.

Chris
 

flashlight

Senior Member
Location
NY, NY
Occupation
Electrician, semi-retired
Also helpful if a fan/light is installed.

Probably more of a common situation than my example.

raider1 said:
If proposal 9-95 passes the comment stage then a grounded conductor will be required at most switch locations in the 2011 NEC.


How many times have you seen where somebody has decided to add a receptacle at what was originally a switch box, and has solved the no neutral problem by bonding a wire to the metal box ? I have seen that at least half a dozen times. I know the code is not written to protect DIYers, but at least this measure would prevent that...
 

iwire

Moderator
Staff member
Location
Massachusetts
This exception should only be applied in cases where compliance with the normal requirements is so difficult that covert attempts to evade the rules would be likely.

What the ......:confused:

So now inspectors have to be able to predict the future?:roll:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
What the ......:confused:

So now inspectors have to be able to predict the future?:roll:

It's such a stupid proposal and waste of natural resources the CMP had to follow suit with something stupid themselves. ;)

I fail to see any safety issue here, it is more of an attempt to make the NEC a design manual

Roger
 

flashlight

Senior Member
Location
NY, NY
Occupation
Electrician, semi-retired
It's such a stupid proposal and waste of natural resources the CMP had to follow suit with something stupid themselves. ;)

I fail to see any safety issue here, it is more of an attempt to make the NEC a design manual

Roger

It was a safety issue when unqualified persons "jerry-rigged" so as to put
a receptacle in a switch box w/o a neutral. But maybe your point is that the NEC is not there to anticipate/avert actions by unqualified people.

Re- waste of resources, that's a good point. Is that also your feeling
about pulling "spare" conductors ?
 
It's such a stupid proposal and waste of natural resources the CMP had to follow suit with something stupid themselves. ;)

I fail to see any safety issue here, it is more of an attempt to make the NEC a design manual

Roger


Sometimes I wonder what the CMP groups are discussing to come up with some new code. This one in particular. Who are they making SAFER with this new code?
 

jimport

Senior Member
Location
Outside Baltimore Maryland
Occupation
Master Electrician
But the CMP can leave obvious inconsistancies in like the branch circuit for the range hood. If it is hard wired it can be on the lighting circuit, cord and plug it needs a dedicated circuit.

I heard that was the intent behind the cord and plug option was so that the circuit was adequate for the possible future usage. Do they think no one would ever change out a hard-wired range hood for a microwave? Hello McFly.
 