i was right!! wow.
i was right!! wow.
Ok, thanks! I was starting to panic.
About the lights flickering/motor startup...how complex an issue is that, and how is 3% involved?
from the same link as my previous comment-
The NEC recommends that the maximum combined voltage drop for both the feeder and branch circuit shouldn't exceed 5%, and the maximum on the feeder or branch circuit shouldn't exceed 3% (Fig. 1). This recommendation is a performance issue, not a safety issue.
So...I realize a 5.1% VD isn't always going to immediately cause all the lights to flicker like crazy, but two things-
1- If you are shooting for 5% on the feeder, does that mean you want to shoot for 0% on the branches?
2- And in a case when there is a transformer involved. From that link again:
What is the maximum length of 6 AWG THHN you can use to wire a 480V, 3-phase, 37.5kVA transformer to a panelboard so voltage drop doesn't exceed 3%?
A: 376 feet.
So 6 AWG is out for a 500 foot run. (copper here)
But am I over-simplifying here- you *could* use 4 AWG for 500 feet/480V/3ph, that would be over 3% but under 5% VD.
However, with 24kVA/100 amps of constant loads (a good 80% of that being motors)... this is where I'm confused- would it be 2, 1, or 1/0 AWG to stop flickering?
I get (1 AWG * 3%) / (1.732 * 12.9 * 100 amps) = 539 feet?
(83680cm * 14.4V) / (1.732 *12.9 *100) = 539.
If I should start a new thread, let me know.
i was right!! wow.
Ok, thanks! I was starting to panic.
About the lights flickering/motor startup...how complex an issue is that, and how is 3% involved?
There is no right or wrong answer here, it comes down to how little voltage drop the customer is willing to pay for / how much voltage drop they can tolerate.
Some folks will live with lights dimming when the AC compressor starts other folks will not.
Now a 200 amp service might never see a constant load over 60 amps but it could see high currents during motor start ups.
from the same link as my previous comment-
The NEC recommends that the maximum combined voltage drop for both the feeder and branch circuit shouldn't exceed 5%, and the maximum on the feeder or branch circuit shouldn't exceed 3% (Fig. 1). This recommendation is a performance issue, not a safety issue.
So...I realize a 5.1% VD isn't always going to immediately cause all the lights to flicker like crazy, but two things-
1- If you are shooting for 5% on the feeder, does that mean you want to shoot for 0% on the branches?
2- And in a case when there is a transformer involved. From that link again:
What is the maximum length of 6 AWG THHN you can use to wire a 480V, 3-phase, 37.5kVA transformer to a panelboard so voltage drop doesn't exceed 3%?
A: 376 feet.
So 6 AWG is out for a 500 foot run. (copper here)
But am I over-simplifying here- you *could* use 4 AWG for 500 feet/480V/3ph, that would be over 3% but under 5% VD.
However, with 24kVA/100 amps of constant loads (a good 80% of that being motors)... this is where I'm confused- would it be 2, 1, or 1/0 AWG to stop flickering?
I get (1 AWG * 3%) / (1.732 * 12.9 * 100 amps) = 539 feet?
(83680cm * 14.4V) / (1.732 *12.9 *100) = 539.
If I should start a new thread, let me know.