goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
What I thought should have been a simple answer to a simple question turned out to have multiple answers from some of my EC colleagues of whom I asked several questions.
I'm repairing/replacing an existing 200A service on a residence. The service comes down the side of the house on the driveway side. The existing service had to be temporarily re-suspended using SEU cable due to a hardy-plank siding installation. The existing service had been run in 2" PVC with (3) 2/0 copper conductors. I want to install new 2" PVC and I'll be using a 90 and a PVC LB on the load side of the meter enclosure and into the existing MBP. The MBP is not being changed. FYI, NJ is still on the 2014 NEC
Here were my questions :
One of my colleagues also suggested I look at section 310.15 (B)(7)(1) thru (4)
Thanks
I'm repairing/replacing an existing 200A service on a residence. The service comes down the side of the house on the driveway side. The existing service had to be temporarily re-suspended using SEU cable due to a hardy-plank siding installation. The existing service had been run in 2" PVC with (3) 2/0 copper conductors. I want to install new 2" PVC and I'll be using a 90 and a PVC LB on the load side of the meter enclosure and into the existing MBP. The MBP is not being changed. FYI, NJ is still on the 2014 NEC
Here were my questions :
- Can I use 2/0 copper THHN for the service ? (Most of my colleagues say no they always use 3/0 for all conductors)
- Can I down-size the neutral 2 sizes to # 1? (most of my colleagues say no)
- Can I use an LB on the load side of the meter where it enters the house ?
- Do I have to use sch. 80 on the load side of the meter where it enters the house ? (Remember it's on the driveway side and can be hit by a car if the HO comes home drunk
)
- Is an LB rated for use with sch. 80 PVC ?
One of my colleagues also suggested I look at section 310.15 (B)(7)(1) thru (4)
So, in reading this I see that if I have a service rated at 200A, 83% of that would be 166A wire rating. Can I then use 2/0 wire rated at 175A ? Can I also drop the neutral down to # 1 ?310.15 Ampacities for Conductors Rated 0–2000 Volts.
(B) Tables.
(7) 120/240-Volt, Single-Phase Dwelling Services and Feeders.
For one-family dwellings and the individual dwelling units of two-family and multifamily dwellings, service and feeder conductors supplied by a single-phase, 120/240-volt system shall be permitted be sized in accordance with 310.15(B)(7)(1) through (4).
(1) For a service rated 100 through 400 A, the service conductors supplying the entire load associated with a one-family dwelling, or the service conductors supplying the entire load associated with an individual dwelling unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the service rating.
(2) For a feeder rated 100 through 400 A, the feeder conductors supplying the entire load associated with a onefamily dwelling, or the feeder conductors supplying the entire load associated with an individual dwelling, unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the feeder rating.
(3) In no case shall a feeder for an individual dwelling unit be required to have an ampacity greater than that specified in 310.15(B)(7)(1) or (2).
(4) Grounded conductors shall be permitted to be sized smaller than the ungrounded conductors, provided that the requirements of 220.61 and 230.42 for service conductors or the requirements of 215.2 and 220.61 for feeder conductors are met.
Thanks