junkhound
Senior Member
- Location
- Renton, WA
- Occupation
- EE, power electronics specialty
other was undersized?
Couple points of reference:
Own house, 5300 sq feet, 200A service.
Have not tripped the 200A in 45 years (QO breakers). Have had a 48A electric pressure washer in use, 2 clothes dryers (about 25 A each), 25 A electric water heater, a 25A oven, and 5T heat pump (40A) all running at same time. Still under 200 A. Could maybe have one of the grandkids over using the pressure washer and start using the 280A stick welder? - maybe exceed 200 A then If all the lights turned on also?
OTOH, son has an 800 sq ft studio with 200 A service, 200A panel was cheaper than a 100 A panel, plus poco won't hook up anything under 200A meter base. e.g.
You may install a service panel or meter base/socket that is sized less than 200 A, but the service line and meter that PSE installs will be sized as if you were installing a 200 A service. If you are installing an underground service that is less than 200 A, your meter base/socket must meet the dimensional requirements for a 200 A underground meter base/socket,..........
OTOH2. POCO installed just a 25 kVA transformer for 5 habitat townhouse units I worked on 6 years ago (gas heat and WH, but electric stove). Each unit had 200 A panel. Our habitat engineer asked them to put in a 50 kVA transformer, but Poco would not put in anything larger than 25 kVA until the 25 kVA ever failed or excess complaints of brownouts. AFAIK, the 25 kVA is still in place.