The 60 KW 3 phase 208/120 generator and 200 amp service rated ASCO transfer switch have arrived and I am getting ready to install them in a few days. The neutral is not switched. (The ASCO has a 200 amp CB for utility connection). I plan on running four 4/0 copper and a #4 copper equipment grounding conductor.
The small office building has a 208/120 3 phase service with a 2 year maximum demand of about 30 KW. In the future they may put on a small addition and add 10-20 KW of load.
The amperage for the 60 KW generator is: 60 KW/208/1.73=167 amps. Here is my question: After unpacking the transfer switch and generator I see that the circuit breaker on the generator is 225 amps. Because the generator output maximum is 167 amps I am guessing/hoping I would not be in violation of any NEC code because of the 225 amp CB on the generator feeding through a 200 amp transfer switch. It is my understanding that the ASCO switch is rated for 200 amps continuous. I can't "simply" increase the size of the transfer switch. The next size is 400 amps and is a ground mounted cabinet versus a post/wall mounted cabinet.
I would appreciate any thoughts on the situation of using a 200 amp service rated transfer switch with a 60 KW generator that has a built in 225 amp circuit breaker. Thanks!
The small office building has a 208/120 3 phase service with a 2 year maximum demand of about 30 KW. In the future they may put on a small addition and add 10-20 KW of load.
The amperage for the 60 KW generator is: 60 KW/208/1.73=167 amps. Here is my question: After unpacking the transfer switch and generator I see that the circuit breaker on the generator is 225 amps. Because the generator output maximum is 167 amps I am guessing/hoping I would not be in violation of any NEC code because of the 225 amp CB on the generator feeding through a 200 amp transfer switch. It is my understanding that the ASCO switch is rated for 200 amps continuous. I can't "simply" increase the size of the transfer switch. The next size is 400 amps and is a ground mounted cabinet versus a post/wall mounted cabinet.
I would appreciate any thoughts on the situation of using a 200 amp service rated transfer switch with a 60 KW generator that has a built in 225 amp circuit breaker. Thanks!