Zane Bailey
Member
As per this article, when the service entrance feeder conductors are paralleled, the equipment bonding jumper is to be sized as per 250.102(C)/250.66.
On separately derived, what size equipment grounding conductor would be needed between the transformer and the first disconnect means in each parallel conduit/
If I have 2 conduits with 4-350kcmil would the equipment grounds in each conduit be 1/0 AWG or 2/0 AWG?
Zane.
On separately derived, what size equipment grounding conductor would be needed between the transformer and the first disconnect means in each parallel conduit/
If I have 2 conduits with 4-350kcmil would the equipment grounds in each conduit be 1/0 AWG or 2/0 AWG?
Zane.