humor me mike.....what makes the image i posted NM Cable?

My point in posting it was to make it clear in a SDS ( not a service ) that the system bonding jumper could be technically at either the SDS itself or the first enclosure ( Disconnect ) of again a single SDS setup....

In my opinion it depends on the location of the GEC to the GE....which can be at either........but not at both.
 

jwelectric

Senior Member
Location
North Carolina
radiopet said:
humor me mike.....what makes the image i posted NM Cable?
Nothing, I was using the scenario of NM cable points out the EGC better than using a pipe


radiopet said:
My point in posting it was to make it clear in a SDS ( not a service ) that the system bonding jumper could be technically at either the SDS itself or the first enclosure ( Disconnect ) of again a single SDS setup....
And this is why there are two Exhibits in the Handbook.


radiopet said:
In my opinion it depends on the location of the GEC to the GE....which can be at either........but not at both.
And this is the bottom line as to what is the System Bonding Jumper.
 