Karl H

Senior Member
Location
San Diego,CA
I don't think a "Clipping" on to a Al. neutral bar is a good idea IMO.




Probably...all of them :grin:

Considering that all ckts are now essentially GFCI or AFCI ~ who cares...the ckt's neutral goes right to the CB...the clip on the CB is making contact with the neutral bar.


I could be wrong on the configuration..I haven't RTFM :smile:

Brochures
Plug into Savings with Plug-on Neutral Loadcenter & AFCI & GFCI breakers (PDF, 856KB)


Plug-on Neutral Loadcenter (PDF, 519KB)
 

Karl H

Senior Member
Location
San Diego,CA
..but "clipping" onto an ungrounded conductor bar/bus is acceptable?

Yes, I don't mind losing power on a MWBC, It's losing the grounded conductor
I'm worried about. Panels that are located outdoors, the Al. bus bar is
going to oxidize and cause problems. Great for us, but as a design I think it's a bad idea. Just look at it, does a clip over a mechanical screw look
like a good connection that will last over time and load? It's just something
I wouldn't sell or recommend when my name is on the install or design
choice, Listed or not. JMHO
 

Sparky555

Senior Member
Is there any point in ignoring T310.15(B)(6) and installing 200A services with 3/0 CU conductors on a typical SFH?

I had an inspector tag a service. He said I used the wrong size wire. I ask for the code he has in front of him and get him to the page# with the table. He said "OK, use 3/0 next time".

It's not worth my time. I stock 3/0 & 3 ga. I don't stock 2/0 & 4 ga. It's not about ignoring the table, it's about the value of my time.
 