IMO, the size would depend on where the connection was made. If you connected the GEC at the meter, I would say you would size it per the service conductors supplying the meter. If you connected at the service disconnect means, I would say size per the service conductors supplying the disconnect.
Again, my opinion.
The SEC's begin at the drop. IMO you need to use the largest size SEC's for sizing the GEC even if they terminate in the 100 amp service panel.
You may already done this but I mention it for benefit of everyone else:
Read art 100 defintions of service entrance conductors.
If supply is overhead the service entrance conductors start at the connection to the service drop.
If supply is underground the service entrance conductors start at point of connection to the lateral - sometimes there is no splice or other connection separating the service entrance conductors and the lateral conductors and is generally considered the point of entrance in that case. If the lateral ends at a meter socket the load side conductors are the service entrance conductors.