Don't you need to bond the conduit both ends between the meter can and panel? Using rigid nipple.
PVC is not allowed in my area. Hence rigid to ground rods and water meter.
I can use #6 to the ground rods?
250.64(E) Enclosures for Grounding Electrode Conductors.
Ferrous metal enclosures for grounding electrode conductors shall be electrically continuous from the point of attachment to cabinets or equipment to the grounding electrode and shall be securely fastened to the ground clamp or fitting. Nonferrous metal enclosures shall not be required to be electrically continuous. Ferrous metal enclosures that are not physically continuous from cabinets or equipment to the grounding electrode shall be made electrically continuous by bonding each end of the raceway or enclosure to the grounding electrode conductor. Bonding shall apply at each end and to all intervening ferrous raceways, boxes, and enclosures between the cabinets or equipment and the grounding electrode. The bonding jumper for a grounding electrode conductor raceway or cable armor shall be the same size as, or larger than, the enclosed grounding electrode conductor. Where a raceway is used as protection for a grounding electrode conductor, the installation shall comply with the requirements of the appropriate raceway article.
Your first sketch is fine per the NEC, just bond the GEC to the bottom end of the RMC, the top is bonded with the locknuts.
Roger
don't you need the bushings if the conduit is connected to a concentric knockout?
don't you need the bushings if the conduit is connected to a concentric knockout?
Still having a hard time getting my head around this.
Would either of these be correct
Option #1
Meter Can
Panel
or
Option #2
Meter Can
Panel
No, but this is a common misconception.
Roger
What about 250.92(A) it is the requirements of Bonding of Services, see (3)
and 250.92(B) is Method of Bonding at the Service see the note under (4)
At a few of the Western sectionals I have been to, this question was brought up more then once and both times the CMP's and UL said the concentric KO's were not listed for grounding of raceways protecting service conductors or GEC's, and cited the above code sections each time.