I thought it might be fun to start a thread with some changes in the 2011. If anyone is interested in discussion and adding others please do so.
I will start with 200.4. This article seems to end the argument of whether or not you can oversize a neutral for more than one set of MWBC.
I will start with 200.4. This article seems to end the argument of whether or not you can oversize a neutral for more than one set of MWBC.
200.4 Neutral Conductors. Neutral conductors shall not be used for more than one branch circuit, for more than one multiwire branch circuit, or for more than one set of ungrounded feeder conductors unless specifically permitted elsewhere in this Code.