We have a contractor that proposes to use four 3/c IAC cable consisting of 3 -750kcm AL and 3-2/0 AL grounds for a 2000A circuit ( we'll adjust the over current device to 1900A ). NEC 250-122 specifies a 400kcmil AL conductor for a 2000A circuit. Table 8 properties list the 2/0 as 133,100 circular mils. Multiplying x3 conductors = 399,300 circular mils. We stated that the 3-2/0's do not meet the circular mil area per the NEC. The contractor now has furnished a letter from the cable manufacture stating "Our cable is UL listed under UL 1569. UL 1569 in turn calls out ASTM B801 ?Standard Specification for Concentric-lay Stranded Conductors of 8000 series Aluminum Alloy for Subsequent Covering or Insulation? to define the physical and electrical characteristics of the conductor. Section 15 of ASTM 801 states ? The cross-sectional area of the conductors shall be not less than 98% of the cross-sectional area as specified in Column 1 of Table 1.? Per code the ground size for a 2000 amp panel is 400kcmil. 98% of 400kcmil is 392kcmil. Our cable construction has 3-2/0 ground phases. Through our manufacturing tolerance we allow for 0 to minus 1% therefore the minimum size of our 2/0 is: 0.99x133,100 = 131,769. Because we have 3-2/0 then the combined circular mil is 395,307 circular mils which is more than 392kcmil.
In other words a conductor that has a cross section of 392kcmil can be called a 400kcmil because it falls within the 2% tolerance. And because the combined circular mil of 3-2/0 is 395,307 CM you can call it a 400kcmil. So in the end 3-2/0 meet the requirement of a 2000 amp panel.
My belief is the cable meets the intent, HOWEVER, no where in the NEC do I find where "allowable percentages" of a cable is permitted for use. Should 3-3/0's be the minimum requirement at 167,800 mil x3 = 503,400 circ mil?
In other words a conductor that has a cross section of 392kcmil can be called a 400kcmil because it falls within the 2% tolerance. And because the combined circular mil of 3-2/0 is 395,307 CM you can call it a 400kcmil. So in the end 3-2/0 meet the requirement of a 2000 amp panel.
My belief is the cable meets the intent, HOWEVER, no where in the NEC do I find where "allowable percentages" of a cable is permitted for use. Should 3-3/0's be the minimum requirement at 167,800 mil x3 = 503,400 circ mil?