I have seen owners/users that don't even know how to turn on one that is working correctly
See complete teardown of the Siemens main breaker unit at
https://forums.mikeholt.com/showthread.php?t=196215
NEC is published every three years. I believe it is too late for any input for changes for the 2020 edition, though they likely have not yet come up with final copies of every change that might be made but are likely close with a majority of them.
50 amp 2 pole GFCI is probably the most popular two pole because it is commonly needed for spa's. Though 2 pole 20 and 30 are sort of common enough they are usually readily available at electrical supply houses.
Not a lot of things out there require GFCI protection if direct wired instead of cord and plug connected, and there is a lot of 15/20 amp 120 volt receptacles compared to other other ratings driving the need for 15/20 amp single pole (or the common GFCI receptacle) to be most commonly demanded GFCI devices.
Do you think what Mike Holt said that it was possible whole house GFCI protection could exist in the future is true? This way we don't have to see many rules where to put it: Simply put it in the entire House. In fact. I am doing just that. My Siemens GFCI breakers protect everything now except the lights and air conditioners.
To the OP. in case you add the single or double GFCI breaker in your main panel. Can you please test if there is spacing between the spring clips and the bus bar? What brand do you plan to get? Square D, Siemens? What are all the available GFCI breaker brands?
Siemens Engineering told me it's normal. They wrote: "
"Sorry for the delay. Engineering has received new breakers from stock, which, when installed are configured the same as you have shown in the photos you sent with the angle on the connections. Engineering has tested & indicate contact is sufficient for proper function of the breakers."
I want to know if the Square D GFIC breakers or other brands are like this too.