- Licensed Electrician
I wanted the NEC to go all in. That's the best way to reveal these things for the fraud they are.I'm glad the AFCI rules were rolled back from the original proposal.
Not the same wording as 2014.I'm interested in seeing the language they use for saying that, but don't have a login. Is it still the language they had in 2014?
(B) Increased in Size. If ungrounded conductors are increased in size to account for voltage drop, wire-type equipment grounding conductors shall be increased in size. The increase in size shall be at least in the same proportion as the increase in the size of the ungrounded conductors using their circular mil area.
That's correct. No more "or if's". Only for voltage drop. It's back to the intent of the original version... with the exception that the original version only required upsizing where a wire-type EGC was required. That is, you originally didn't have to upsize if you used a metallic raceway wiring method.Well, it is quite an improvement in my opinion, as it now gets straight to the point of the intent of the rule.
So now you no longer have to upsize EGC, if you've upsized the main conductors because you had left-over wire that is larger than necessary, kicking around from a previous job. Or if you've prepared for 60C terminations in your design worst-case-scenario, and end up with 75C terminations as is the industry norm. Or if you have equipment that specifically calls for larger than necessary wire.
Are you saying that under the older wording, if you had both a wire-type EGC and a metallic raceway EGC, you didn't need to upsize the wire-type EGC?That is, you originally didn't have to upsize if you used a metallic raceway wiring method.
Yes, but IIRC we're talking like back in the '70's.Are you saying that under the older wording, if you had both a wire-type EGC and a metallic raceway EGC, you didn't need to upsize the wire-type EGC?
Cheers, Wayne
So if I have 10 awg conductor for de-rating purposes and install a 20 amp overcurrent protective device then I can use a #12 equipment grounding conductor?
Cheers, Wayne
Ok , so if you are using a cable size 8 NM and upsize to 6nm . It won't work as #8 and #6 use the same size #10 if I recall correctly.
Yep.So if I have 10 awg conductor for de-rating purposes and install a 20 amp overcurrent protective device then I can use a #12 equipment grounding conductor?
Under the prospective wording, depends on the reason for the upsize... which you did not clarify. If the reason is not for voltage drop, yes it will work.Ok , so if you are using a cable size 8 NM and upsize to 6nm . It won't work as #8 and #6 use the same size #10 if I recall correctly.
That's essentially what this means...It would work when his area adopts the 2017 NEC, until then no regardless of the claimed reason.
Under the prospective wording...