2017 NEC Subpanel (not in building)

Status
Not open for further replies.
Location
Florida
Occupation
EC
does the 2017 code require 2 ground rods for a subpanel when it is located outside (not in a building). also what is the code article pertaining to this?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
does the 2017 code require 2 ground rods for a subpanel when it is located outside (not in a building). also what is the code article pertaining to this?
The requirement for ground rods at a separate building was in the NEC when I started in the trade in 1978, and likely many years before that.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
This is similar to your earlier thread and the answer will be the same if it is the same question.

 
Location
Florida
Occupation
EC
the situation is a main panel containing 20 spaces and feeds rv sites. a 100 amp sub panel was added about 110 feet away from the point of service. all of which don't attach to any buildings. the new 100 amp sub panel is free standing and will service 3 rv spots as well as a pole barn made of wood. again there isn't a building for any of the panels.
 
Location
Florida
Occupation
EC
in that since every rv location would require a GEC. each rv site has a panel with single 20 single 30 and 2 pole 50 breakers. that would put 300 ground rods in just so satisfy that.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
in that since every rv location would require a GEC. each rv site has a panel with single 20 single 30 and 2 pole 50 breakers. that would put 300 ground rods in just so satisfy that.
Sounds like somebody is going to get a good work out.
 