thanks for the clarification.The OP was referring to a 320 base like that, but with disconnects also built into it - a 320 amp meter main.
thanks for the clarification.The OP was referring to a 320 base like that, but with disconnects also built into it - a 320 amp meter main.
230.85 Emergency Disconnects.
For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped. Each disconnect shall be one of the following:
- (1)
Service disconnects marked as follows:
EMERGENCY DISCONNECT,
SERVICE DISCONNECT- (2)
Meter disconnects installed per 230.82(3) and marked as follows:
EMERGENCY DISCONNECT,
METER DISCONNECT,
NOT SERVICE EQUIPMENT- (3)
Other listed disconnect switches or circuit breakers on the supply side of each service disconnect that are suitable for use as service equipment and marked as follows:
EMERGENCY DISCONNECT,
NOT SERVICE EQUIPMENT
Markings shall comply with 110.21(B).
Hmmm... interesting. Reading 225.30 it seems to me a lot of services I have seen may have been in violation of your second point - one 320A meter feeds two separate 200A disconnecting means with OCP, which in turn feed two separate panels on the same building. I assume it was done this way because 400A switchgear is more than twice the cost of 200A equipment.There are two things going on here: One is the separate enclosure requirement for service disconnects (although seems to be a bit more lax for meter assemblies, then being separate "compartments"). The second is the "only one feeder to supply a building" requirement, which as far as I know has no recently changed in the code.
Hmmm... interesting. Reading 225.30 it seems to me a lot of services I have seen may have been in violation of your second point - one 320A meter feeds two separate 200A disconnecting means with OCP, which in turn feed two separate panels on the same building. I assume it was done this way because 400A switchgear is more than twice the cost of 200A equipment.
Could it possibly mean that a building can only be supplied by one feeder from a given service disconnecting means, and if there are two discos there can be two feeders? That seems like a bit of a reach from the letter of the code, which says ,"...feeder on the load side of a service disconnecting means..." (emphasis mine, and it's from the 2011 NEC, the only one I have handy).
Hmmm... interesting. Reading 225.30 it seems to me a lot of services I have seen may have been in violation of your second point - one 320A meter feeds two separate 200A disconnecting means with OCP, which in turn feed two separate panels on the same building. I assume it was done this way because 400A switchgear is more than twice the cost of 200A equipment.
Could it possibly mean that a building can only be supplied by one feeder from a given service disconnecting means, and if there are two discos there can be two feeders? That seems like a bit of a reach from the letter of the code, which says ,"...feeder on the load side of a service disconnecting means..." (emphasis mine, and it's from the 2011 NEC, the only one I have handy).
225.30(B) Common Supply Equipment.
Where feeder conductors originate in the same panelboard, switchboard, or other distribution equipment, and each feeder terminates in a single disconnecting means, not more than six feeders shall be permitted. Where more than one feeder is installed in accordance with this section, all feeder disconnects supplying the building or structure shall be grouped in the same location, and the requirements of 225.33 shall not apply. Each disconnect shall be marked to indicate the load served.
I hope we are still talking about the 2020 NEC
Article 225 is about outside branch circuits and feeders not services and the way I read it I can have 6 feeder to a structure if the all come from the same panelboard etc. This section quoted (225.30) is a new section
It has never been a violation, nor is it in the 2020 to have a 320 meter base with 2 main disconnect panels outside that feed 2- mail lug panels indoor.s
I agree, assuming the disconnects are physically mounted on the building. If the disconnects are remote, I would disagree. Where the disconnects are mounted on the building it is no different than a large commercial building with multiple feeders to panels scattered around the building....
It has never been a violation, nor is it in the 2020 to have a 320 meter base with 2 main disconnect panels outside that feed 2- mail lug panels indoor.s
Never was compliant.Quite frequently I see a 320A meter feeding two 200A discos (or feedthrough panels with 200A main breakers) out on a rack some distance from the house feeding a pair of MLO panels on the house. Are you saying that this isn't or won't be NEC compliant?
My statement here was referencing a service that is located remote from the structure with feeders going to the structure, not ON the structure.Not attempting to pirate MH’s info on the subject,
Looking at the 2020 code and his book and video on the topic again this morning;
it looks like I would be ok to install a 320 meter/main (Siemens product I mentioned) that has 2 - 200 amp breakers and run 2 feeders to the structure as long as they end up terminating in separate discos that are located outside the structure and are grouped? The clincher is that the feeders have to originate from the same panel board! (If I’m understanding things correctly!)
With new content in 230.71(B) the meter with two mains would need to have the two mains in separate compartments of the assembly to comply with this section. None of the ones I have ever seen in the past will comply, guessing manufacturers will be changing design but may or may not have product available soon enough for some and you will probably be using two separate main breaker enclosures when on the building supplied. In a situation like you are describing where it is away from the building supplied, you are out of luck until they make an assembly with separate compartments because you must run them multiple feeders from the same panel, switchboard, etc.Not attempting to pirate MH’s info on the subject,
Looking at the 2020 code and his book and video on the topic again this morning;
it looks like I would be ok to install a 320 meter/main (Siemens product I mentioned) that has 2 - 200 amp breakers and run 2 feeders to the structure as long as they end up terminating in separate discos that are located outside the structure and are grouped? The clincher is that the feeders have to originate from the same panel board! (If I’m understanding things correctly!)
Here if the POCO is providing?maintaining that disconnect at the pole they don't consider it to be the service disconnecting means. POCO can and at times will change that disconnect to whatever is convenient or common for them to use at the time, it may be fused, circuit breaker or non fused equipment it gets replaced with then that changes what may or may not be extended from it code wise. So AHJ here has deemed it is just a point on the system that is convenient to the POCO for interconnection to customer wiring and convenient disconnecting means to isolate customer from utility without calling technicians out to disconnect the supply. We don't need to run an EGC from this point and all conductors leaving this point are still considered to be service conductors.My statement here was referencing a service that is located remote from the structure with feeders going to the structure, not ON the structure.
I live in a rural area where sometimes the service is not located at the structure , but might be located at the power pole where the poco xfrmr is located, then feeder(s) go to the structure.
Here if the POCO is providing?maintaining that disconnect at the pole they don't consider it to be the service disconnecting means. POCO can and at times will change that disconnect to whatever is convenient or common for them to use at the time, it may be fused, circuit breaker or non fused equipment it gets replaced with then that changes what may or may not be extended from it code wise. So AHJ here has deemed it is just a point on the system that is convenient to the POCO for interconnection to customer wiring and convenient disconnecting means to isolate customer from utility without calling technicians out to disconnect the supply. We don't need to run an EGC from this point and all conductors leaving this point are still considered to be service conductors.
With new content in 230.71(B) the meter with two mains would need to have the two mains in separate compartments of the assembly to comply with this section. None of the ones I have ever seen in the past will comply, guessing manufacturers will be changing design but may or may not have product available soon enough for some and you will probably be using two separate main breaker enclosures when on the building supplied. In a situation like you are describing where it is away from the building supplied, you are out of luck until they make an assembly with separate compartments because you must run them multiple feeders from the same panel, switchboard, etc.
Sorry but no! The AHJ can call anything they want service equipment but if is on the utility side of the demarcation point only the name in the National Electrical Safety Code (NESC) has any legal effect on what it is for code enforcement purposes. Do keep in mind that the enforcement of the NESC is the exclusive province of the State's utility regulating agency. I have never encountered any electric utility that will allow me to touch anything that they install or maintain.Here if the POCO is providing?maintaining that disconnect at the pole they don't consider it to be the service disconnecting means. POCO can and at times will change that disconnect to whatever is convenient or common for them to use at the time, it may be fused, circuit breaker or non fused equipment it gets replaced with then that changes what may or may not be extended from it code wise. So AHJ here has deemed it is just a point on the system that is convenient to the POCO for interconnection to customer wiring and convenient disconnecting means to isolate customer from utility without calling technicians out to disconnect the supply. We don't need to run an EGC from this point and all conductors leaving this point are still considered to be service conductors.
If your AHJ calls it the service disconnect then it is what it is and you need to apply things as worded in code.
Isn't there a kind of "gotcha" there in that, since neither of those separate feeders is the entire supply to the building, you cannot use the wire sizes called out in the residential service conductor sizing table. In other words do each of those feeders have to be sized by the general ampacity table rather than using the reduced sizes normally allowed for residential buildings? Obviously I think that is true but I wanted to check with the rest of you to see if I'm reading that correctly.Washington has a exception to NEC that allows multiple feeders to a building, was six , was was increased recently. Reason was a 400 amp Class 320 service at head of driveway would require 400 amp feeder. We allow multiple smaller feeders as 200A is much less than single 400 amp. Feeder disconnects must be grouped on bldg.