well, one fear I have about the disconnects is the problem of theives or vandals, which is very common on homes...but also note a section of the proposed code.. this will not be service equipment rated... so, if ot is not service equipment it cannot be between the meter and the main breaker... but instead must have the main breaker installed ahead of it. So, you are talking a high amp variation of a three way switch loop, meter to main breaker, main breaker to firefighter disconnect, firefighter disconnect to breaker panel for #poco, and then somehow running the solar or wind or water power through another firefighter disconnect located in same area...As currently written the rule does not permit any type of remote disconnect, one of the reasons it that the rule is intended to remove all power inside of the building. A remotely operated disconnect that is inside the building does not do that.
All of this done to make it easy for the firefighters to disconnect power at one spot, in theory, which also aids the thieves and vandals, but adds costs to the homeowner or builder, and, in reality, if one thinks about it, unless relays are used, low voltage ones for safety reasons, ie: 12 to 24 volts DC... you still have the probability of live wires in the structure or on the roof of the structure, especially when you have people such as myself who can and do modify grid tied gear such as microinverters to run off grid...
The use of low voltage relays means yes, there is still low voltages, 12 to 24 volts, present for the responders, but hopefully they will be trained in how to fully safe a solar system when working around it on a roof...IE, disconnect the quick connects at teh panel groups or switch off the various combiner boxes... as they move around them. Given the heights involved in my own area to get to the roofs, I am sure that mainly first responders would be the ones up on the roofs rather than thieves as the roof hight in my area averages 30 feet above ground...
Also, in my own area, breaker panels are normally on an inside wall, not an outside wall, in a hallway, due to the single thickness walls. Double walls like used in USA and UK are not normal..only cavities in walls here are those left by not filling the blocks with cement.
So, I would want to see remote switching allowed to shut down the various panels, especially with the no more than six disconnect rule as some of the homes I have dealt with have four breaker panels, each with its own generator or solar interlocks, plus a main panel, plus all the inverters etc... a big trick here is to use a few panels on microinverters specifically for the water pumps to bring the water from underground tanks to roof tanks , tricked to run in daytime from aan ac circuit running from another part of the systems in the house, or to run it directly from DC if a dc water pump was found from the suppliers... Since this is a dedicated system of only two to three panels, sometimes one panel even, and no actual breaker boxes run by some of the people, how to disconnect this without running a remote disconnect is one of the things I need to figure out as I see this way more than some people would think... I am in a country where people have to keep at least a weeks water on site, and where the local water company only supplying water to your neighborhood once per week or twice per week is considered a good water service..lol..