I guess my point is CMP-2 is arrogantly pushing this requirement on incompatible equipment and the result is non enforcement. How does that make it safer?
Because when the equipment doesn't "play well" with the GFI it trips.
JAP>
I guess my point is CMP-2 is arrogantly pushing this requirement on incompatible equipment and the result is non enforcement. How does that make it safer?
I did no such thing Ryan Jackson just said in his video that the branch circuit starts at the final overcurrent device and ends at the utilization equipment why wouldn't he say it ends at the outlet?I think that’s a valid point.
And you didn’t need to corrupt the NEC definition of “outlet” to make it!
Because he is trying to explain to people like you what the term "outlet" actually means.I did no such thing Ryan Jackson just said in his video that the branch circuit starts at the final overcurrent device and ends at the utilization equipment why wouldn't he say it ends at the outlet?
I know what an outlet is and hardwired utilization equipment is not an outlet.Because he is trying to explain to people like you what the term "outlet" actually means.
No, the complete equipment is never the outlet, but with hardwired equipment the outlet is part of the equipment.I know what an outlet is and hardwired utilization equipment is not an outlet.
Factory wired equipment is not covered by the scope of the NEC that is why utilization equipment is "sometimes" hardwired to outlets. My public comments will clarify it very well in the next cycle.No, the complete equipment is never the outlet, but with hardwired equipment the outlet is part of the equipment.
Per the NEC I want to add an informational note that on hardwired equipment the utilization equipment termination compartment be referred to as an appliance outlet and add that definition to article 100.No, the complete equipment is never the outlet, but with hardwired equipment the outlet is part of the equipment.
We are not talking about factory wired equipment. We are talking about the premises wiring connection to any type of hard wired equipment. If the equipment is hardwired, the outlet is at the equipment.Factory wired equipment is not covered by the scope of the NEC that is why utilization equipment is "sometimes" hardwired to outlets. My public comments will clarify it very well in the next cycle.
Why is it not defined as the appliance outlet? Ryan said the branch circuit ends at the utilization equipment that is not always the end of the premises wiring so not all branch circuits connect to an outlet.We are not talking about factory wired equipment. We are talking about the premises wiring connection to any type of hard wired equipment. If the equipment is hardwired, the outlet is at the equipment.
Also you need to start with Public Inputs, not Public Comments.
How is the end of the branch circuit conductor not the end of the premises wiring for a hard wired circuit?Why is it not defined as the appliance outlet? Ryan said the branch circuit ends at the utilization equipment that is not always the end of the premises wiring so not all branch circuits connect to an outlet.
The claim was that the branch circuit ends at the outlet the utilization equipment connects to.How is the end of the branch circuit conductor not the end of the premises wiring for a hard wired circuit?
There is no need for a specific definition of appliance outlet and even if there was such a definition, it would leave out a lot of hard wired commercial and industrial equipment that are not appliances.
Supposedly the outlet location on hardwired utilization equipment can't even be illustrated that's why Mike has an illustration that points at nothing.How is the end of the branch circuit conductor not the end of the premises wiring for a hard wired circuit?
There is no need for a specific definition of appliance outlet and even if there was such a definition, it would leave out a lot of hard wired commercial and industrial equipment that are not appliances.
You are welcome to submit a PI. Might be tricky submitting any specific wording that will get accepted as a change.Supposedly the outlet location on hardwired utilization equipment can't even be illustrated that's why Mike has an illustration that points at nothing.
There are similar problems with the definition of a branch circuit and a feeder. Why this is the chew toy you decided is the one you don't want release from your jaws is a mystery to me. I agree that the rule to GFCI protect outdoor hard wired equipment is stupid, but the time and energy wasted on arguing about it in terms of the outlet location is wasted.The claim was that the branch circuit ends at the outlet the utilization equipment connects to.
I disagree with it being a waste of time it was the grounds behind the State of Colorado completely deleting 210.8(E) and 210.8(F) for the 2023 cycle. CMP-2 got greedy with the public input written by Nehad Elsharif that was supposed to apply to all hardwired equipment installed at a dwelling unit. It was written due to a death on an ungrounded mis-wired A/C unit and the code is written for new installations and replacements not unlicensed repair work. CMP-2 got greedy to expand class A protection due to a definition that I believe almost exclusively applies to cord and plug connected equipment. My public inputs whether they pass or fail will clarify this misinterpretation due to the definition of individual branch circuit not mentioning the connection to an outlet and the creation of 210.8(D) which covers all specific appliances regardless of vintage, cord and plug connected or hardwired why didn't they simply say where connected to an outlet?There are similar problems with the definition of a branch circuit and a feeder. Why this is the chew toy you decided is the one you don't want release from your jaws is a mystery to me. I agree that the rule to GFCI protect outdoor hard wired equipment is stupid, but the time and energy wasted on arguing about it in terms of the outlet location is wasted.
CMP-2 knew there were problems with 210.8(F) and they did nothing to address it in the last cycle so now the result is as if it never was changed.There are similar problems with the definition of a branch circuit and a feeder. Why this is the chew toy you decided is the one you don't want release from your jaws is a mystery to me. I agree that the rule to GFCI protect outdoor hard wired equipment is stupid, but the time and energy wasted on arguing about it in terms of the outlet location is wasted.
Your discrepancy with definition of "outlet" has nothing to do with what their intent was. They still have what they wanted whether most of us agree with their decision or not. In 2023 only change was to add an exception with an expiration date with the hope that the HVAC manufacturers will have something by then that plays well with GFCI's. TIA for 2020 effectively was same thing. They ultimately want GFCI protection on pretty much all utilization equipment outdoors at dwelling units other than luminaires as mentioned, but won't be surprised to see those included down the road either.CMP-2 knew there were problems with 210.8(F) and they did nothing to address it in the last cycle so now the result is as if it never was changed.
Are you aware that the UL standard allows 10ma of leakage current even beyond 2026? If the CMP's intent was to include all hardwired utilization equipment in the change their plan went fatally wrong when they claimed EVSE was governed by another code panel and GFCI protection is not required regardless of location of install that screws up CMP-2s argument.Your discrepancy with definition of "outlet" has nothing to do with what their intent was. They still have what they wanted whether most of us agree with their decision or not. In 2023 only change was to add an exception with an expiration date with the hope that the HVAC manufacturers will have something by then that plays well with GFCI's. TIA for 2020 effectively was same thing. They ultimately want GFCI protection on pretty much all utilization equipment outdoors at dwelling units other than luminaires as mentioned, but won't be surprised to see those included down the road either.
I don't know what UL standards are. If you are correct apparently the CMP doesn't know or doesn't care either.Are you aware that the UL standard allows 10ma of leakage current even beyond 2026? If the CMP's intent was to include all hardwired utilization equipment in the change their plan went fatally wrong when they claimed EVSE was governed by another code panel and GFCI protection is not required regardless of location of install that screws up CMP-2s argument.
I'm sure other states will do similar at least for the near future, but looks like NEC is set on keeping what they have for now and ultimately seems to think they will be able to remove the exception down the road.CMP-2 will be diminished in the next code cycle and 210.8(F) will be deleted the State of Colorado AHJ is not going to pick and choose what equipment is compatible and requires protection.