The "Inconvenient Truth" ... but you have to wait until September 1, 2026.
mtnelect HVAC & Electrical Contractor Location Southern California Occupation Contractor, C10 & C20 - Semi Retired Feb 19, 2023 #141 The "Inconvenient Truth" ... but you have to wait until September 1, 2026. Attachments TIA Log No. 1653, HVAC GFCI, 05-27-2022.pdf 652.6 KB · Views: 18
Bill Snyder NEC expert Location Denver, Co Occupation Electrical Foreman Jul 16, 2023 #142 acrwc10 said: If you have an exterior meter/main combo that has conduit feeding directly to an AC unit, where is the outlet ? Click to expand... If you look at the definition of individual branch circuit it states from the final OCPD to utilization equipment no mention of it connecting to an outlet.
acrwc10 said: If you have an exterior meter/main combo that has conduit feeding directly to an AC unit, where is the outlet ? Click to expand... If you look at the definition of individual branch circuit it states from the final OCPD to utilization equipment no mention of it connecting to an outlet.
roger Moderator Staff member Location Fl Occupation Retired Electrician Jul 16, 2023 #143 Sorry but this thread has run it's course, we will know the conclusion in 26