Can you feed a 240V subpanel from a 208 3p panel using a 2P breaker?
QES said:Can you feed a 240V subpanel from a 208 3p panel using a 2P breaker?
QES said:Can you feed a 240V subpanel from a 208 3p panel using a 2P breaker?
Simpsonelectric said:No it is not 3 or 1 phase 208V. They are 1 phase panels 240V
Thanks
Steve Simpson
iwire said:Yes. :smile:
Jim W in Tampa said:Anything to back that up with ?You saying i cant have single phase lights ?
I figgured that and see no problem with itSimpsonelectric said:I am sorry, I seem to have to gotten into another thread. I was speaking of dock power.
Steve Simpson
QES said:Can you feed a 240V subpanel from a 208 3p panel using a 2P breaker?
Simpsonelectric said:Well I don't think you can. If the dock plug is rated 230 volts you have to supply 230 volts. The rating of the recept. In my case I do have some (3) 3 phase large pedistals that can be fed from one of my 3 Phase 208 V panels and the plugs are rated 208 volts stamped right on them.The 230 volt ones are all fed from a 230 volt, single phase transformer.
Steve Simpson