208v to 120/240v

One of the posters here called it an RV or a Caravan which is similar for the UK version. We wouldn't have used the in a house. C'est la vie.
I don't think you are understanding. The RV has a house/breaker panel IN IT that is similar to the breaker panel IN a house.
By similar, I mean the 50A RV panels have a 240V supply, but all the loads are 120V. The 240V supply just gives them more available 120V loads.
The 30A RV panels only have a 120V supply.
RV=Recreational Vehicle
 
I don't think you are understanding. The RV has a house/breaker panel IN IT that is similar to the breaker panel IN a house.
By similar, I mean the 50A RV panels have a 240V supply, but all the loads are 120V. The 240V supply just gives them more available 120V loads.
The 30A RV panels only have a 120V supply.
RV=Recreational Vehicle
Yes, I know what an RV is. The confusion was in the domestic residence rather than RV. They are two things.
 
In this polyphase case, I simply mean that the primary circuit and secondary circuit share some of the coils and that there is no galvanic isolation from primary to secondary. So you can have coils of different phases (coils on different cores) electrically in series.
So how's this for a broader definition of autotransformer: there is a copper path (including transformer coils) from every output side conductor to an input side conductor? I agree your proposed arrangement meets that definition.

Also, does galvanic isolation mean "there are no such paths" or instead "any output conductor with such a path is grounded"? Or something else?

Cheers, Wayne
 
Also, does galvanic isolation mean "there are no such paths" or instead "any output conductor with such a path is grounded"? Or something else
Isolated means isolated. This is the starting point.
However, the NEC requires bonding separatly derived 120V systems to ground. Which kind of negates total isolation. But the normal current carrying conductors are still isolated until a fault occurs.
 
Also, does galvanic isolation mean "there are no such paths" or instead "any output conductor with such a path is grounded"? Or something else?

Cheers, Wayne

For transformers, I think a fair definition is 'galvanic isolation means there are no conductive paths between primary and secondary internal to the transformer. A grounding connection may create a conductive path outside of the transformer.' Or perhaps 'In a transformer arrangement with galvanic isolation, intentional grounding breaks the galvanic isolation between systems. In an autotransformer arrangement, there can be no galvanic isolation because transformer coils are shared between primary and secondary systems.'
 
In this polyphase case, I simply mean that the primary circuit and secondary circuit share some of the coils
Do you mean this literally, as in if you draw the primary circuit (consisting of the primary supply equipment, some conductors, and some subset of the coils) and the secondary circuit (consisting of some subset of the coils, some conductors disjoint from the primary conductors, and the load equipment), then there is at least one portion of one coil that is common to both circuits?

In other words, say you have a 120V:120V transformer, and you supply the primary with L-N 120V, and the secondary terminals are L'-N' respectively, and you connect N' to L, so that L' is at 240V to N. If your secondary conductors are N and L' to make a 240V grounded 2-wire supply, that's an autotransformer. While if your secondary conductors are L' and N', that's not an autotransformer, you've just created a weird 120V 2-wire supply referenced to ground but with neither secondary grounded.

Is that the usual terminology?

Cheers, Wayne
 
Top