208V to 230V buck boost
cppoly
New York
If an appliance is 230V and there's only 120/208V available from a panel, would a buck boost transformer would be needed?
For a 2,300 watt, 230V load, this would be a 3 kVA transformer, which is 3,000 / 208 = 14.4 amps * 1.25 = *1.25 = 18 amps = 20 amp OCPD primary?
Then, would a 20 amp disconnect fused at 15 amps be needed on the secondary?
I would, and, simply put the boost transformer between the OCPD and the appliance it is serving.
Jap>