Jmays
Member
- Location
- Oceanside, CA, USA
Hello all, I have read numerous posts on the subject, but wanted to get specific verification on our calculations for a 208 to 240 boost, since I have not worked heavily with autotransformers. Thanks in advance.
This is a light industrial warehouse. This unit is fed by 208/120 WYE 3 phase 4 wire service (line/line/line/neutral/ground). We need a circuit dedicated for a single phase 240v welder.
We will be using a Acme T113074 buck booster. Primary coming from a double pole 40amp breaker runs to the BB, secondary will be a 240v receptacle. So primary OCDP only.
The BB boosting the needed 32v to achieve 240v is rated at 11.25 Kva/46.90 Amps. Which is plenty for the required load of 40amps. 8awg from the panel to the BB and from the BB to the receptacle.
I don't think I'm missing any pertinent info. Please let me known if I did.